Upgrade of fat braid main earth conductor
S
SW1970
Hi folks, about to do a domestic PIR and observed during survey that the main earth conductor is flat braided copper. Didn't measure but from photo it looks either 6 or 10mm2 CSA. Assuming that Captain Adiabatic tells me it's inadequate, when I call on supplier to upgrade, will they most likely replace with larger braid or put on a new sheath clamp with appropriate round cable? Many thanks, SW
Here you go...
Did you get the measurements of it?
Nominal area (mm²)Width (approx. mm)Thickness (approx. mm)Wire diameter
[TD="class: table_content_left"]6[/TD]
[TD="class: table_content"]12.0[/TD]
[TD="class: table_content"]1.0[/TD]
[TD="class: table_content"]0.20[/TD]
[TD="class: table_content_left"]10[/TD]
[TD="class: table_content"]15.0[/TD]
[TD="class: table_content"]1.5[/TD]
[TD="class: table_content_left"]16[/TD]
[TD="class: table_content"]19.0[/TD]
[TD="class: table_content"]2.5[/TD]
[TD="class: table_content_left"]25[/TD]
[TD="class: table_content"]25.0[/TD]
[TD="class: table_content"]3.0[/TD]
[TD="class: table_content_left"]35[/TD]
[TD="class: table_content"]4.0[/TD]
[TD="class: table_content_left"]50[/TD]
[TD="class: table_content"]30.0[/TD]
[TD="class: table_content"]5.0[/TD]
[TD="class: table_content_left"]70[/TD]
[TD="class: table_content"]32.0[/TD]
[TD="class: table_content"]6.0[/TD]
[TD="class: table_content_left"]95[/TD]
[TD="class: table_content"]37.0[/TD]
[TD="class: table_content_left"]120[/TD]
[TD="class: table_content"]45.0[/TD]
[TD="class: table_content_left"]150[/TD]
[TD="class: table_content"]50.0[/TD]
[TD="class: table_content"]8.0[/TD]
[TD="class: table_content_left"]200[/TD]
[TD="class: table_content"]10.0[/TD]
It's the DNO property mate and all you can really do is call them, but I know that if you have a good Ze value for it they will do nothing.
If I got a good Ze value, then I would basically leave it alone, You could note it, but it's not part of our installation so as long everything the customer side is ok then your good.
It may even be an old DIY TN-S done by a bygone sparks
i=p/u, no, it's not just a water pipe. Why would an electrician post a picture of a supply cable with an earth strap around it and ask what the DNOs approach would be if it was a water pipe? Let me quote you something:
"aint easy isit, dealing with cable pullers like myself. ive no expierience with testing so just done R1+R2 with multimeter"
A 16mm2 earthing conductor is not strictly required if the adiabatic equation allows it. But, I had not appreciated, per malcolm's comment, that this may be a DIY TN-S, in which case, the DNO would state they are not supplying an earth. What would happen then if there was an incident (this property has no RCD). If I'd done a job and walked away, yes, I probably be liable.
One needs to be very careful giving technical advice or commentary on a forum like this. Because a DIYer, an apprentice or someone with little experience might (foolishly) take the advice and then go and kill themselves or someone else.