Upgrading my garage supply. | on ElectriciansForums

Discuss Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net

Joined
Aug 17, 2017
Messages
28
Reaction score
2
Location
Chippenham
Hi Everyone,
I moved into a new build house 1 year ago.
I’ve got round to investigating the supply to my separated garage.
At the house the builders have fitted a fused spur (non switched) internally onto a ring circuit fused at 13amp.
From this is a short length of 2.5 T&E going externally to a plastic Ip66 mounted external JB.
From this a 1.5 SWA is run underground to the garage and terminated into a metal clad switched fused spur inside the garage.
A double socket is connected to the spur on the incoming side.
The lighting circuit is connected to the load side and the fuse is 5amp. The switched spur therefore acts as the light switch.

The SWA has an earth conductor but the armourings are not earthed separately in the plastic JB. No banjo is fitted at the metal clad spur but the back box is bonded to the earth core.

Questions on existing instal.
Should the internal spur have a switch providing DP isolation before it leaves the house?
Should the armourings be earthed by bonded banjos to the earth core at both ends?

Planned changes.
I would like to replace the metal clad switched spur with a new garage CU with a main isolator with RCD and 2 x MCB’s fitted. 6amp for lighting and 10amp for sockets.
I then plan to wire multiple sockets around the garage in plastic conduit with LNE singles.

Would there be any issues in doing this as in my mind I’m providing DP isolation in the garage with RCD protection and separate rated MCB’s for lights and sockets?

Appreciate any comments?
 
not much point in putting additional RCD in garage because if new build should already be in the house(check),could maybe change spur to double pole so as to be able to isolate in the event of fault in garage,sockets in garage already on 13 amp fuse so not much point in changing to mcb/garage unit,maybe easiest to just extend socket circuit in garage from socket already there,SWA should be earthed.
 
the non switch feed from you existing circuits should be 2.5mm SWA to the garage not 1.5mmSWA considering you have a light and socket feed from s/fs in the garage
. not bright sparks who put that in, and you want to alter the circuit in that garage .
 
Last edited:
its like the film jaws (need a bigger boat) in order for you up grade in the garage a new cross sectional of SWA and separate feed for your garage from the c/u if possible.
 
Why do you require "multiple sockets"?
 
not much point in putting additional RCD in garage because if new build should already be in the house(check),could maybe change spur to double pole so as to be able to isolate in the event of fault in garage,sockets in garage already on 13 amp fuse so not much point in changing to mcb/garage unit,maybe easiest to just extend socket circuit in garage from socket already there,SWA should be earthed.
Hi Kenny, thanks for the first sensible answer.
When you say should be earthed, I thought the same but does it have to be earthed as if it does I can have the builder on that?
I know about the 13a supply but again do they have to provide DP isolation on the spur or is this a nice to have?
The Garage CU I was looking at has a 30ma RCD incuded in the DP isolator, so was just going to use it as its there.
The 6 & 10a are there for further discrimination and I want to wire additional lights in 1.5 and additional sockets in 2.5 singles.
 
Hi Kenny, thanks for the first sensible answer.
When you say should be earthed, I thought the same but does it have to be earthed as if it does I can have the builder on that?
I know about the 13a supply but again do they have to provide DP isolation on the spur or is this a nice to have?
The Garage CU I was looking at has a 30ma RCD incuded in the DP isolator, so was just going to use it as its there.
The 6 & 10a are there for further discrimination and I want to wire additional lights in 1.5 and additional sockets in 2.5 singles.

Hi,with double pole spur you will be able to isolate garage in the event of a neutral earth fault in garage to stop house RCD tripping,with more than one RCD on the circuit it will be pot luck wich one trips first if not both,changing to mcbs wont make much difference to discrimination,swa should be earthed
 
If it is easy enough to get a cable from your consumer unit to the garage, install a 4 or 6mm2 SWA and feed it with a MCB to a RCD protected garage Consumer unit.

That will give you plenty juice for garage items, lights, sockets, tools, electric door etc.
 
Hi Kenny, thanks for the first sensible answer.
When you say should be earthed, I thought the same but does it have to be earthed as if it does I can have the builder on that?
I know about the 13a supply but again do they have to provide DP isolation on the spur or is this a nice to have?
The Garage CU I was looking at has a 30ma RCD incuded in the DP isolator, so was just going to use it as its there.
The 6 & 10a are there for further discrimination and I want to wire additional lights in 1.5 and additional sockets in 2.5 singles.

answer to the above, in red. the steel wire armouring of the SWA MUST be earthed, even if not used as a protective conductor for the cable, the supply end must be earthed, generally by use of a SWA gland and banjo or earth nut. you can pull the builder upon that.
 

Reply to Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
197
The 3A fuse is there to protect the current lighting. For additional power you connect from the non protected 3A fuse side.
Replies
1
Views
562

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top