Upgrading my garage supply. | Page 2 | on ElectriciansForums

Discuss Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net

answer to the above, in red. the steel wire armouring of the SWA MUST be earthed, even if not used as a protective conductor for the cable, the supply end must be earthed, generally by use of a SWA gland and banjo or earth nut. you can pull the builder upon that.

Thank you you are quite right i should have said MUST not SHOULD
 
answer to the above, in red. the steel wire armouring of the SWA MUST be earthed, even if not used as a protective conductor for the cable, the supply end must be earthed, generally by use of a SWA gland and banjo or earth nut. you can pull the builder upon that.
Thanks Tele.
So what about DP isolation at the spur, I know its a nice to have to totally isolate outside, but is it a must that they should've supplied this or not?
 
Hi,with double pole spur you will be able to isolate garage in the event of a neutral earth fault in garage to stop house RCD tripping,with more than one RCD on the circuit it will be pot luck wich one trips first if not both,changing to mcbs wont make much difference to discrimination,swa should be earthed
Why not, surely a lighting fault will trip a 6a MCB before a 13amp fuse?
 
Why not, surely a lighting fault will trip a 6a MCB before a 13amp fuse?
Hi - descrimination between protective devices is an interesting topic. For a short circuit fault where you will have say 500A current, it would be a bit of a race but quite likely the 6A MCB will trip and the 13A fuse will also melt. For an overload fault where lighting was drawing say 18A then the 6A MCB should trip only.
 
Existing installation has a 5A fuse for the lights and a 13A fuse for the sockets... I don't see the problem.
I have also asked the OP why we are discussing this in private messages and also on the post...
 
My apologies I don't use this forum very often and I think ive hit "quote in conversation" rather than reply.
My mistake sorry.
I just wanted to tidy up the install and provide separate circuits to wire from in the garage rather than the all on the 13amp spur in the house.
It would just seem wrong to me to be wiring the sockets from the incoming side and lights from the load side of the fused spur in the garage.
Forget costs and time, I have these at my disposal.
Other than having 2 x RCD's in series (I understand both or either could trip) am I not improving the install by providing MCB protection in the garage.
I am electrically trained a long time ago on industrial kit and have never done domestic regs, so I was searching to find out if:-
a. The builder should've earthed the armoured at one or both ends?
b. Should he have provided DP isolation on the outgoing external supply?

The install doesn't easily allow for replacement of the armoured with 2.5 or to take straight to the house CU.
I'm trying to make the best of a poor job.
 
Mr Freeze, what do you intend to use the garage for and the load requirements?
 

Reply to Upgrading my garage supply. in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
197
The 3A fuse is there to protect the current lighting. For additional power you connect from the non protected 3A fuse side.
Replies
1
Views
562

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top