W

waitees

Hi all

just doing a board change tested everything which was fine. Gone to turn everything on a loads of faults !

Downstairs lights , immersion and ring circuit in kitchen can get rcd to stay on with these off, what's strange is I can switch something on and it trips both rcds .

Could someone point me in the right direction and what to start with first ? This has not happed before.

Also when I turn the cooker on fine light inside comes on when turn the heat up on the cooker it trips straight away , cooker faulty ?
 
Sounds like maybe neutrals in wrong RCD sides hence tripping ???

Also maybe borrowed neutrals.

Did you carry out a test prior to change? This is very important, as it will unveil these problems.

I had a similar problem once, and I refused to carry out board change due to underlining problems like borrowed neutrals etc.

Good luck anyway mate and hope you can sort it out. Try testing each circuit individually, IR, R1+R2, Zs etc

Best regards,
Sav
 
10 way wylex with 2 rcd, 1 at 63a other 80a , done quite a few if these boards, never had problem , must have been lucky.

Testing was all fine.

Any ideas :( ?
 
Last edited by a moderator:
Hi again,
is this a new board your using as its a bit weird to have 1 RCD 63a and another 80a ( not that it matters I suppose ).

Are the RCD's Wylex as well??

Sav
 
Hi Mate, Some boards come pre wired with a link between the two neutral bars, have you checked for this and if so remove it.
Hope this helps KJ

 
 
also check the rcd neut is wired to the correct bars, could be crossed,

more likely borrowed neutrals and million other problems at property - pays to do some basic tests pre change
 
Hi again,

The tripping of the RCD by the downstairs lighting circuit hints at a borrowed neutral - probably on your two way lighting.

The 'immersion' and 'ring circuit' tripping the RCD hints at neutrals in wrong bar.

The link in the CU (suggested by Keith) is a good point, but if the RCDs are holding with just three circuits turned off, then I think unlikely.
 
Now, the rcd won't go on even tho all the breakers are off and the other rcd is off and main switch is on, what could it be ?????
 
Try changing the RCD for a new one. Sounds like the kit you got is faulty, hence they gave you one 63a and one 80a RCD. They probably made up the kit with left overs !!

If this fails, I would remove RCD's (like 16th edition boards). and put evrything on the appropriate mcb's so that you can switch on and go home!!

Then tomorrow get 2 new RCD's, but test the install beforehand.

Sav
 
Are you sure your neutrals are correct?

Is it possible to post a picture up? It will help a great deal?.
:(




I have seen an 80amp and a 63amp RCD in a 17th edition board many times... However I can't remember if it was wylex or mk? These are the only 2 I use domestically..
 
Last edited:
Try changing the RCD for a new one. Sounds like the kit you got is faulty, hence they gave you one 63a and one 80a RCD. They probably made up the kit with left overs !!

If this fails, I would remove RCD's (like 16th edition boards). and put evrything on the appropriate mcb's so that you can switch on and go home!!

Then tomorrow get 2 new RCD's, but test the install beforehand.

Sav

Really??



By the way, Sav, here is one of many:)

Toolstation > Electrical > Circuit Protection > Volex 17th Edition Dual RCD Consumer Unit
 
Last edited by a moderator:

Reply to Urgent rcd !!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top