Yes sorry thats if they are differen't if they are the same either could trip
 
What is the CSA of the SWA conductors? Don't see any real issue in it being 2 core, just needs glanded off properly.

What size of MCB is protecting the SWA?
 
No issues at all D80 but metal to metal joints with ring/locknuts could break down in time if in a damp situation.
The 3rd copper core won't.
 
No issues at all D80 but metal to metal joints with ring/locknuts could break down in time if in a damp situation.
The 3rd copper core won't.
i've been on a couple of breakdowns where water has penetrated into a conduit box and rotted through copper conductors. the steel armour was intact in both cases.
 
I've done the 2391 thought it wasnt too bad just didn't click about 2 rcds in series not something mentioned just need more experience. Not learnt anything about surge protection either yet.

Watchers dropped off abit so probably crack back on when its picked up.
 
I've done the 2391 thought it wasnt too bad just didn't click about 2 rcds in series not something mentioned just need more experience. Not learnt anything about surge protection either yet.

Watchers dropped off abit so probably crack back on when its picked up.

That's where a qualification is only worth having when backed up with years of experience.
 

Reply to Using twin & earth for sub board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
166
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Twin and earth on its own isnt going to meet the requirements for burial. Why not use Swa ?
Replies
1
Views
451
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top