srl-8
Hi guys,
i have changed a fuse board today in a outbuilding/large shed (it has a kitchen and shower and lounge etc.. a )
It is a TT system with earth rod.
My ZE reading was 187 ohms - now the regs state I am ok upto 200, so I assumed this was ok.
All the R1 + R2 and insulation resistance came back normal.
When I carried out the ZS tests, the reading were very high, for example:
Shower circuit on a 40a MCB - 2.6 omhs !
Kitchen Ring on a 32a mcb - 2.7 omhs !
same for lounge and bedroom rings.
I have checked to regs and these figures are over the maximum allowed.
Any advice ???
what or who...lol....no seriously he`s a VERY well respected member in here matey.....although when i explained to my cousin (from hull) that the gentleman i was buying the books from`s avatar was "widdler"...well he thought that really funny.......good deal though so i aint complaining.....
To the OP.....ignore this.
There is nothing wrong with the UK max Ra of 200 ohms, as long as your system is protected by RCD's,preferably an up front 100ma S type at the origin,and 30ma protection to final circuits...a single rod with an Ra of 187 ohms is perfectly adequate and acceptable.
Unless you achieve a sub 2 ohm Ra you are wasting your time attempting to improve it...ie,if you drive in more rods and achieve 10 ohms,an Ra most would consider very low,your PEFC will be 23a...not a lot of use for most OCPD's,you are still reliant on the RCD for earth fault protection so you may as well have left it at 187 ohms.
As already stated,your Zs readings are low..(not high)...due to parallel paths through bonding etc and are acceptable.
Absolutely agreed, what is this weird obsession with trying to obtain TN values on a TT system?
Someone will post a reply regarding unreliable RCDs, I'll ask for just 1 example of a death or injury from this scenario, none can be found!
The reg's, BS 7430 (earthing) and Guidance Note 8 are perfectly clear and logical regarding TT Ra values.
And the above is basically why, the UK has crap TT systems and always will do, with the perpetuation of some of the stupid comments such as these two examples...
200 ohms from a 1m rod is about as useful as using a bent screwdriver to tighten a screw, be it for the Ra or it's stability! The UK's obsession with this crazy figure of 200ohms (which is based only on stability) is about as far from logical as you can get. No other country that i know of, has or mentions such a high limit, of anywhere approaching that figure. Yet both of you are trying to defend it!! It is indefensible and that section of the Reg's is in dire need of a revision. ...In fact there was talk of a lowered figure being pushed for inclusion into the last batch of amendments...
No-ones trying to obtain disconnection times equal to a TN system, but that's not by any means an impossibility either. But the lower an Ra is, the better the chances of having a protective device trip in a relatively decent enough time, not to cause fire or maybe possible injury, despite a non-functioning cure-all RCD... Great if you have parallel earths from water/gas bonding to help you along, well until they come along and replace with plastic that is...
And yes your quite right, RCD's DO fail and a lot more often than either of you will, or care to admit too. Just because YOU haven't read anything about an RCD causing fire, injury or even a death, doesn't mean it hasn't happened, can't happen, won't or will happen!! Smugness like this, just doesn't become you!!!
What a sorry state the UK TT systems are these day's, ...in the past it was nothing to find many if not most old TT systems with Ra's 5 ohms or lower, even 10 ohms was considered to be on the high side, (even the Yanks talk about trying to improve a 20 ohm Ra with an additional Rod!!) Yet here we are talking in the realms of 200 ohms, and even experienced electricians trying to defend this as all fine and dandy. Why, because we now have the cure-all RCD devices, Oh, ...and it's written in there all seeing all knowing bible, so it must be good-un!! ...lol!!
I had one the other day on an EICR...RCD let go alright ..on test that is....but came to the manual (push button) test at the end of the 6.....wouldn`t let go......an instant condemnment.....
Geezus, is this still going. It's getting a bit like War & Peace:tounge_smile:
There's far more fiction here than there ever was in War & Peace, I back up my arguments with all available statistics, British Standards and years of experience installing perfectly safe TT installations that meet the requirements of those standards.
Of course, the requirements are guided minima and if anyone wants to fill up a garden with copper to slavishly attempt to attain Ra values akin to a TN system then go for it but at least ponder beforehand the futility and costs of the task!
anybody would think you were going to "fill a garden up" with gnomes ...then link em all up in series............whatever happened to depth???......
You'd need some depth to get to TN values in most UK soils!
I'd take a 400 Ohm Ra reading on a 2.4M rod anytime rather than 50 Ohms on a 1M rod though, depth is indeed king!
E54 keeps mentioning this 1M rod as if that's all anyone here uses!
agreed on the depth thing IQ......better to have a higher Ra ...with stability...than a lower one...but only a shallow rod......until the sun pelts down of course..lol...watch it rocket..lol...
And that's where depth comes into it, you are seeking depth to get past the level of drying and freezing, both of which will compromise your Ra values.
so why do we keep seeing these shallow rods ....all connected in series...as if thats gonna do owt..lol.....
Very Hi ZS Reading on TT system? any advice
Australia
srl-8,
malcolmsanford,
TrueNAS JBOD Storage Server