View the thread, titled "Very high r1+r2 readings and Zs in conduit?" which is posted in UK Electrical Forum on Electricians Forums.

K

Kev2632

Hi,

Why would I be getting very high r1r2 readings and Zs readings in a water heater circuit wired in the existing conduit when the house was built back in 19oatcake...? Would the conduit have anything to do with it and if so? Why?

Thanks
 
with the CSA of the conduit in which its wired, will that allow it too have such a high reading? or would that normally give a very low reading if the conduit is " sound", because the CSA area is bigger so it should in theory have alot lower reading than the R1+R2 of live to earth in twin and earth yea??
 
yea i'll give that a go, but would the CSA of the conduit have anything to do with it? or would that normally make the readings alot lower yea? is that right?
 
Is the conduit earthed correctly at the consumer unit? Does the consumer unit connect into the conduit? is the consumer unit plastic by any chance? Are all the other circuits earthed using the same wiring method?

we are all sat at home in front of keyboards with a beer cos nothing is on TV.

We need the maximum amount of info if we are to help.

AND, when you do get it sorted, come back on here and tell us what the problem was so we can all learn!
 

Reply to the thread, titled "Very high r1+r2 readings and Zs in conduit?" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top