well, nick's just suggested 1 Meg. that's the trial and error part. try 1 Meg., and if it's no improvement, try a lower value. ( not too low, of course ). the combined R/C snubbers may well give a better result.
 
Clamp the cable and see what current has been induced, then you can work out the value. Discrete components from RS/Farnell/Maplins.
 
ive noticed on here recently problems with leds staying on when switches are off not had any problems my self and fitted quite alot whats the general feeling of why there staying on just in case it happens to me look a fool if you cant tell customer why its happening
 
Just trying to re-ignite this one as I'm back there tomorrow to have a go at it.

I'm going to start by taking all the LED lamps out of the circuit, and test again for the voltage. If it is still present (which I'm sure it will be) I'll then start taking the circuit apart.

The thing that is bugging me is that with ALL the light switches of the circuit off, I still get 74v at this particular down light fitting. And I also get approx 58v at the bathroom light fittings.

As said before all the neutrals are in Wago's, the wiring is new, all the conductors are meggering at >499 (I tested at 1000v to make sure). I've meggered the switches, taken the switches off and connected the wires into Wago's.

ANY ideas would be good just for me to try them. The more I think about it the more confuddled I get.

Many thanks for taking the time to read this.
 
if it's induced voltage you won't be able to fix it as long as cables run together.
 
Do you really think it could be an induced voltage of 74v?? and coming from the black strapper to the grey strapper but by-passing the earth wire?
Quite possibly. We're guessing you effectively have the equivalent to this as the overall circuit: http://cappels.org/dproj/simplest_LED_flasher/Simplest_LED_Flasher_Circuit.html with the 3 core for the two way lighting behaving as the capacitor.

The length of one of the strappers will dictate how high a value capacitor you in effect have (the longer the run the higher the capacity) and hence the PD present. You'll find the timing between flashes is a regular period (if only a long time between flashes).

The addition of a snubber resistance will increase the overall resistance to the point where there is insufficient current flow for the led lamps. It can eliminate it completely (but too high a resistance would mean no current flow at 230V either!).

So in this particular case probably not induced from an adjacent circuit, rather from that same circuit; so the only other way to eliminate it would be to run the strappers and common separately (separated by a greater distance, so then no capacitance build up).
 
did have a problem with commercial hair dryers giving the user a shock when they un plugged them , the suppression capacator was across the incomming side of the switch so was holding charge after it was switched off an zapped any one when unplugged and they touched the pins easily rectified 20 hair dryers later relocated the capacator to the other side of the switch , and wrote to the manufacturers too
 

Reply to Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It does seem to me that there's a capacitively coupled voltage to each set of downlights (on the light side of the switch), and when you put the...
Replies
6
Views
425
Similar queries here previously, eg: Advice (please) regarding suppressor / "snubber" for LED lighting | on ElectriciansForums -...
Replies
1
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top