Voltage at light fitting that is turned off | Page 4 | on ElectriciansForums

Discuss Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Limited choice on the packaging front. I'd probably go for this given your 2K2 Ohm choice: Buy High Power RESISTOR 50W 2K2 Vishay RCH50S22000JS06 online from RS for next day delivery.

Easy to solder some leads on for use and wrap in heatshrink for use. Should be easy enough to incorporate in the box(es).

Hi, I managed to get hold of these and they seemed better than the first lot I got hold of, I wired one up to a plugtop to see how hot they got. It lasted for about ten minutes, didn't get too hot, but then burnt it's self out.
Speaking to someone at the wholesaler and they have suggested that I could put an SES lampholder with a oven lamp in the ceiling void which will take the excess voltage out of the switch live.

Good Idea??

I'm not too sure. It would probably work but I dont fancy leaving something like that in the celing...

Is there any other suggestions that anyone can come up with?
 
Burnt out? What did you use as a heatsink?

Errrmmm?? Nothing....

I just left it on the floor, to do it's merry business. It expanded slightly on the back, then it cracked and stopped working.

I really have no idea with this. I wouldn't have thought it needed a heatsink as surely it would have said it needed it on the paperwork?
 
Data from the spec:

Power at 25°C50W with heatsink, 5.5W without heatsink
Resistance Tolerance±5%
Temperature Coefficient≤1Ω ±250ppm/°C, >1Ω ±150ppm/°C
Operating Temperature-55°C → +125°C
Thermal Resistance1.0°C/W
Limiting Element Voltage1285Vac
Overload Voltage2500Vac (Max.)
Dielectric Withstand Voltage3.5KVac
Insulating Resistance10000MΩ
Length50 mm
Width29.4 mm
Height15 mm
 
This is getting silly.

The customer has low energy lighting, 2 X 7W was mentioned. To stop the slight glimmer a loading resistor is suggested which if we go with the first suggestion of 2K2ÎŹ which will dissipate about 19.5W of waste heat. Near three times the lighting load.

It’s making a mockery of “energy saving”.

Would it be possible to fit a single halogen somewhere in the circuit? At least it would do something useful.
 
This is getting silly.

The customer has low energy lighting, 2 X 7W was mentioned. To stop the slight glimmer a loading resistor is suggested which if we go with the first suggestion of 2K2ÎŹ which will dissipate about 19.5W of waste heat. Near three times the lighting load.

It’s making a mockery of “energy saving”.

Would it be possible to fit a single halogen somewhere in the circuit? At least it would do something useful.

Thank you Tony, that is exactly what I have been thinking.

So talking to another wholesaler we came up with this; wiring a 25a modular contactor/relay in the smallest possible enclosureand placing this in the ceiling void.
Wring the switched live to A1 then link that to the top terminal 1, wiring the light from the bottom terminal 2, then wiring the neutral to A2 then linked to the light fitting.

This will enable the contactor coil to take the 74v constantly without pulling in the contacts, and when the switch is live this will then pull in the coil and the contacts switching the lights on.

Any thoughts on this??

I know putting it in the ceiling void isn't the best idea, but there is no other place to fit it as the house is finished. But it's alot better then sticking a pigmy lamp in the void as mentioned before!!
 
It would work and your loading would come down from 33.5W with the resistor to 21W. You could use an octal base relay, they are only 5W.
 
Thanks you brain boxes ,i have been in the trade for 50 years and only the other day came across this induced/ghost voltage for the first time ,thought i was going mad ,you have proved me wrong just seniel i expect ,no sterile, Regards Ronky
 

Reply to Voltage at light fitting that is turned off in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It does seem to me that there's a capacitively coupled voltage to each set of downlights (on the light side of the switch), and when you put the...
Replies
6
Views
425
Similar queries here previously, eg: Advice (please) regarding suppressor / "snubber" for LED lighting | on ElectriciansForums -...
Replies
1
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top