Hi All wonder if anyone can help just wondering how sorting out voltage drop works in practice the regs say that this can be worked out using the Zs or using diagrams. Any idea how this is done in practice?:6:
 
Its not done in practice, its calculated using the values given in the regs. GN3 is very usefull on all things testing, well worth buying if you're serious about doing any sort of electrical work IMO
 
nothing to do with Zs or diagrams, in the osg you will find the mV/A/m values for various cable sizes. then yo take that value, say, for ease of understanding we'll call it "mA". then:

vollt drop = (mA x A x L) /1000 , where A is the design current, L is the length of the circuit.
 
nothing to do with Zs or diagrams, in the osg you will find the mV/A/m values for various cable sizes. then yo take that value, say, for ease of understanding we'll call it "mA". then:

vollt drop = (mA x A x L) /1000 , where A is the design current, L is the length of the circuit.

That's exactly what I thought but was keeping quiet in case there was something I had missed at college haha 
 
When testing why not use R1+Rn
formula as follows; R1+Rn * 1.2 * Lb

Where R1+Rn = overall resistance of phase and neutral conductor
The 1.2 being the correction factor for operating temperature
Lb being the load

Simples
 
When carrying out the continuity tests on the protective conductor of a circuit you will record either an R1+R2 or an R2.

You can use the result of this test to work out the length of the circuit using the resistance/meter values in Table 9A (page 166 OSG).

Once you have the length and design current of a circuit you can then work out the expected Voltage Drop using tables in the OSG or BS 7671.

As an example, let's say you have a 16A radial circuit wired in 2.5mm² T&E.

You do an R1+R2 test and record a value of 0.98Ω.

Now, using Table 9A in the OSG you can work out the length of the circuit.

From the table the resistance of 2.5mm² line and 1.5mm² cpc (R1+R2) is 19.51mΩ/meter.

So, if you divide the result of the R1+R2 test by this value it will give you the length of the cable.

0.98 ÷ (19.51 ÷ 1000) = 50.2 meters.

Now you have the length and design current you can work out voltage drop.

From Table 6D2 (page 130 OSG) the voltage drop per amp per meter for 2.5mm² cable is 18mV/A/m so total voltage drop would be (18 x 16 x 50.2) ÷ 1000 = 14.45V. The maximum voltage drop for power circuits is 11.5V(5%) so the circuit would not comply.
 
Last edited by a moderator:
hi teletrix just wondering how that works with part six of the regs that talks about diagrams and Zs measurements...thats what I dont get??
 

Reply to Voltage Drop and Regs-how do you do it? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
283
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
273
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
721
  • Question
I see, thank you!
Replies
4
Views
588

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top