I built a metal desk with wood top. I just wired in a 500W heat lamp on the desk.
13A plug goes to a single metalclad socket via 1.5mm2 3 core cable.
Same cable then goes from socket to 1 way metalclad switch.
Same cable then goes from switch to heat lamp.
Earths are all connected to each other and to back boxes.
When I take my multimeter and measure between the socket screw and the metal desk I get about 10V. When I turn the heat lamp on it reads about 25V.
Is that normal? Is that something to be worried about? Metal desk is not earthed.
Thanks in advance.