I am currently using a strip connector to connect my cooker, hob and dishwasher to a radial circuit. This has come loose on a number of occasions and so I am considering replacing this setup with Wago 773-173 connectors. These can only facilitate 3 conductors but I have 4 to deal with . It has been suggested to me to use 9 of these connectors set out in three groups of three each.. The first group of three will be connected to the radial circuit and send wires to the second group of three and the third group of three. The second group will be used to send power the the hob and dishwasher and the third group will send power to the cooker.
Thoughts on this setup would be appreciated.
 
I am currently using a strip connector to connect my cooker, hob and dishwasher to a radial circuit. This has come loose on a number of occasions and so I am considering replacing this setup with Wago 773-173 connectors. These can only facilitate 3 conductors but I have 4 to deal with . It has been suggested to me to use 9 of these connectors set out in three groups of three each.. The first group of three will be connected to the radial circuit and send wires to the second group of three and the third group of three. The second group will be used to send power the the hob and dishwasher and the third group will send power to the cooker.
Thoughts on this setup would be appreciated.
It sounds like a terrible setup to be honest.
 
Wago now do a lever version of connectors that will take up to 6mm2 cables, 221-615 for the 5-way one. These are rated to 41A.

However, you don't say what kind of hob this is. I'd be a bit wary of what you propose if this is an electric hob running quite a few kW and sharing the circuit with both an oven (the "cooker"?) and a dishwasher.
 
On the surface of what you say, I would say each of the items you mention should be on their own separate circuit supplied by a switched fused spur. Depends on the rating of each item. I would hazard that if you cannnot make a secure connection (...has come loose on a number of occasions...) then you are outside of your skill set and would advise getting in an electrician.
 
On the surface of what you say, I would say each of the items you mention should be on their own separate circuit supplied by a switched fused spur. Depends on the rating of each item. I would hazard that if you cannnot make a secure connection (...has come loose on a number of occasions...) then you are outside of your skill set and would advise getting in an electrician.

Where do you get switched fused spurs to take 4.6kW and 5.5kW, Vort?
 
oven and hob on a "standard" 32A/6mm circuit, 45A isolator and dual outlet. dishwasher plugged into RFC. like millions of households that have never caught fire. "do it once, do it right".
 
I thought every appliance in France tended to be on its own radial, hence why most dishwashers and the like are conveniently rated at 10A?
Not completely au-fait with French wiring regs, this is just an observation based on what I've seen. Big CU's with plenty of dual pole mcbs often labelled up as dedicated ccts per appliance?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Wago 773 173 advice please
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Bill Johnstone,
Last reply from
Mike Johnson,
Replies
15
Views
3,159

Advert

Back
Top