Hi All, Doing a big remedial job on a factory and changing main incoming tails to 240mm. On inspection found there was no bonding to water and gas. Surely that doesnt mean i need 60mm bonds? also does the clamps HAVE to be bonded next to the incoming water and gas meters or is there a 'get out clause' where you dont have to do it?? If so this could end up being a 60metre run :saddam:

Thanks in advance
 
They are lime kilns. The pipes you can see are mainly gas.

My old workshop is the open door with the red sign above it in the bottom RH corner.
It’s 20+ years since I crashed the land rover in to the door, it’s still got the steel straps I put across the back to hold it together!
The 11KV substation is on the roof.

The place looks a death trap , just pray i dont do the PIR for it lol.
only kidding :)
 
The place looks a death trap , just pray i dont do the PIR for it lol.
only kidding :)

It’s covered by M&Q statutory testing. So don’t worry, you won’t get the call.

What do you mean a death trap? It was perfectly safe if you knew what you were doing.

When I started on the plant all the switchgear was 50+ years old. Hidden in it’s heart are six new transformers (total 5.5MW) and boards along with seven new sub boards (400 or 630A feeds to each). Fourteen new MCC panels, (over 600 drives). I became a dab hand at making off 195mm or re-making .3” paper leads. Some of the time it was like trying to keep a museum running. You had to be inventive with some repairs, spares? What are they?

I enjoyed myself there. It was an absolute s**t hole but still fun, I stuck it for 23 years.
 
I'm just thinking outside the box here.....When running bonding to gas and water it's permisable to use one cable and link the two providing there is no break in the cable. By connecting your bonding to the steel work and then again connecting the steelwork back to a bonding cable to connect to the services, are you not effective doing just this?
 
Use an eylet crimp again and secure either by nut and bolt or tap a hole into the steel. 10mm tapped hole and a C10 eylet would provide a good connection.
Oh, and don't forget the safety electrical connection, do not remove label!
 
The main reason for the bonding conductor being continuous if only one is used, is so if you disconnect one temporarily for maintenance you don't lose both if it is put back incorrectly, or not put back at all.

I suppose a crimped one fulfils the same requirement, also if structural steel is used I suppose you would have either individual local conductors to each service, or a single one crimped as above, same requirements apply.
 
By linking the gas and water using your method, you could effectively remove the bonding tag from the first services and keep continuity to the second; (I would point out however, I would still not break the connection and use lugs, but instead strip the pvc and connect in / out to the first tag to ensure continuity to the second should anything happen to the first)

By using the steel structure method, you will not get continuity to the service should the bonding to the steel be disconnected / damaged?
 
There's a warning notice against removal, and damage, well, that can happen anywhere in any installation but if you're sensible in where you make the connection then the risk can be somewhat less.

Its only the same as the initial bonding of the structural steel.
 
By linking the gas and water using your method, you could effectively remove the bonding tag from the first services and keep continuity to the second; (I would point out however, I would still not break the connection and use lugs, but instead strip the pvc and connect in / out to the first tag to ensure continuity to the second should anything happen to the first)

By using the steel structure method, you will not get continuity to the service should the bonding to the steel be disconnected / damaged?


That's exactly what I meant, both cables crimped into a single lug, whether cut or not will still be continuous if crimped together.

Well removing any bonding conductor for any reason carries this risk, we can only put the safety connection tag on, and hope whoever does the removal put's it back correctly.
 
Well removing any bonding conductor for any reason carries this risk, we can only put the safety connection tag on, and hope whoever does the removal put's it back correctly.

This is the part that does not sit well for me. This would be the equivellent of running a bond to your water pipe, then putting a second 951 tag on the same water pipe and running it to the gas?
 
This is the part that does not sit well for me. This would be the equivellent of running a bond to your water pipe, then putting a second 951 tag on the same water pipe and running it to the gas?

I was referring to the second part of your post here, with respect to the bonding conductor from the MET to the structural steel, and I hear what you are saying here, I suppose this would in effect be two or more connections, one at the MET end, and one or more at the services end.

I suppose it would require a risk assessment, but as others have said it seems to be industry standard.
 

Reply to Water and gas Bonding on three-Phase in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top