R

rosewood

Hi All, Doing a big remedial job on a factory and changing main incoming tails to 240mm. On inspection found there was no bonding to water and gas. Surely that doesnt mean i need 60mm bonds? also does the clamps HAVE to be bonded next to the incoming water and gas meters or is there a 'get out clause' where you dont have to do it?? If so this could end up being a 60metre run :saddam:

Thanks in advance
 
Where do you get the figure of 0.05 Ώ from for an industrial situation?
Start using the structural steel and the figures will drop far lower. This is where a Ductor comes in to it’s own. Readings down to 0.0005 Ώ will be found.
 

Reply to Water and gas Bonding on three-Phase in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top