For single phase its easy Amps = Watts/Volts.

Is it as easy for 3 phase?

Amps = Watts/Volts/3 per phase.

or is there a root 2 in their somewhere?

I need to know to calc the voltage drop along the supply.

Thanks in advance for any offers.
 
Thanks. So from your formulea I need 10.2 amps per phase (call it 11). Now have I got this correct:

I'm allowed 6% voltage drop. 6% of 230 = 13.8volts.

at 11 amps = 1.2545 volts/amp

at 40 meters = 1.2545 / 40 = 0.0313636 volts / amp/ meter = 31 mV/A/M

and according to table 4D2B col 4 this can be achieved with 1.5mm cable.

1.5mm cable run using Reference Method C (clipped direct) can support 17.5 A. So I install a 16A 3 Phase type C MCB and off I go. Right?

Thanks for any comments.
 
Last edited:
Thats far to close, a type c 16 will allow LOTS more than 17.5 amps through it ( ok i forgot how much more )for a short duration of time, if your cable max is 17.5......... I wouldnt sleep at night.
 
Thats far to close, a type c 16 will allow LOTS more than 17.5 amps through it ( ok i forgot how much more )for a short duration of time, if your cable max is 17.5......... I wouldnt sleep at night.

MCB curves.

Type B 5 Times overload current rating for about 30 minutes.
Type C 10 times and type D 20 times.

Cheers............Howard;)
 
Thanks. So from your formulea I need 10.2 amps per phase (call it 11). Now have I got this correct:

I'm allowed 6% voltage drop. 6% of 230 = 13.8volts.

at 11 amps = 1.2545 volts/amp

at 40 meters = 1.2545 / 40 = 0.0313636 volts / amp/ meter = 31 mV/A/M

and according to table 4D2B col 4 this can be achieved with 1.5mm cable.

1.5mm cable run using Reference Method C (clipped direct) can support 17.5 A. So I install a 16A 3 Phase type C MCB and off I go. Right?

Thanks for any comments.

Double check your volt drop values

5% for power
3% for light

3% for lights because of the high frequency stuff being useed.
 
Last edited:
Thanks. So from your formulea I need 10.2 amps per phase (call it 11). Now have I got this correct:

I'm allowed 6% voltage drop. 6% of 230 = 13.8volts.

at 11 amps = 1.2545 volts/amp

at 40 meters = 1.2545 / 40 = 0.0313636 volts / amp/ meter = 31 mV/A/M

and according to table 4D2B col 4 this can be achieved with 1.5mm cable.

1.5mm cable run using Reference Method C (clipped direct) can support 17.5 A. So I install a 16A 3 Phase type C MCB and off I go. Right?

Thanks for any comments.

You need to write in to the IET - You've put a whole new spin on cable selection.:D

I don't think you're supposed to select your cable based on volt-drop.

I thought it went something like this (briefly):

You take the design current and select your cable, taking into account the installation/reference method.
Then, having selected your cable, you select your protective device.
Then, take your design current and cable length and volt drop rating (mV/A/m) and calculate your volt drop - and compare this to what is allowed.
 
Also, an alternative way to work it out is to divide by 3 then divide by 230.

Eg 12kW / 3 = 4kW 4kW / 230 = 17.39A

using the I=P/(Vx1.732) equation 12000/(400x1.732) = 17.32A


Ok, you don't get the identical answer, but it's as near as damnit.

However, I normally use the 1.732 method.
 
Last edited by a moderator:
Also, an alternative way to work it out is to divide by 3 then divide by 230.

Eg 12kW / 3 = 4kW 4kW / 230 = 17.39A

using the I=P/(Vx1.732) equation 12000/(400x1.732) = 17.32A


Ok, you don't get the identical answer, but it's as near as damnit.

However, I normally use the 1.732 method.
Close enough for me Steve! 4.0mm.
 
Last edited:
Well I came in to appologise for the way I expressed somthing earlier today. But since half the posts relevant to this topic have been lost I'm afraid I can't. Sorry about that.
 
Well I came in to appologise for the way I expressed somthing earlier today. But since half the posts relevant to this topic have been lost I'm afraid I can't. Sorry about that.


There seems to be posts going missing everywhere at the moment.......I'll have a look into it.:)
 
Last edited by a moderator:
MCB curves.

Type B 5 Times overload current rating for about 30 minutes.
Type C 10 times and type D 20 times.

Cheers............Howard;)

Are you completely sure that these MCB's will hold with that kind of overcurrent? As far as I was aware, those overcurrents are for an instantaneous trip... Have a look at your trip curves at the back of your BRB.
 
sirkits origional post is correct it acounts for inrush current such as a motor starting ect or high frequency stuff. They will take the much larger inrush current for a longer period but not indeffinatly.
 

Reply to Watts to Amps in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
278
  • Question
Hi There How did you get on with your basement project?
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top