I have a 4-wire well pump (red, yellow, black, and green) which just quit. Cycling normally, then shut off and never came back on. I've gathered that yellow is the common, red is the leg for the start winding and black is the run winding. I've got a couple ohms (4-ish on my trusty Harbor Frieght multimeter which I do not trust to be very precise) on both the start and run windings, so I suspect the pump is actually okay. I've verified I have power through the pressure switch as L1 and L2 in my control box have 240V. I have 120V to ground on red, yellow, and black (with pump connected, mind you) which is good, but neither the red nor black have any voltage to yellow, thus neither winding is actually powered. So, what is my culprit here? Did my overload disconnect die on me? Did I lose a capacitor? Is my relay stuck in run?
 
So, I feel a bit silly. I did not realize that overload disconnect had a manual reset button. It on the bottom of my control box pretty far down inside a concrete cylinder that houses my well. The issue was 100% the overload disconnector cutting off L1. It metered as open and was an obvious issue. When I went for the screws to remove it and saw the button. Face-palm.
 
So, I feel a bit silly. I did not realize that overload disconnect had a manual reset button. It on the bottom of my control box pretty far down inside a concrete cylinder that houses my well. The issue was 100% the overload disconnector cutting off L1. It metered as open and was an obvious issue. When I went for the screws to remove it and saw the button. Face-palm.

Glad you got it sorted! Sometimes it's the simplest things that we overlook.
 
So, I feel a bit silly. I did not realize that overload disconnect had a manual reset button. It on the bottom of my control box pretty far down inside a concrete cylinder that houses my well. The issue was 100% the overload disconnector cutting off L1. It metered as open and was an obvious issue. When I went for the screws to remove it and saw the button. Face-palm.
Well congratulations
 

Reply to Well Pump Control Circuit Troubleshooting in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain...
2
Replies
23
Views
1K
Good luck with your project and welcome to the forum
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top