ExArmy

-
Joined
Jul 27, 2010
Messages
716
Reaction score
143
Location
cumbria
testing a house today before I put RCD protection on it and i got 300mA earth leakage. appox 100mA from the sockets, 180mA on the downstairs lighting circuit, then 20 odd mA accross the rest of the circuits.

I had a poke around the downstairs lighting circuit, couldn't see anything obvious, did R2 tests at all points (OK), did IR test and it was in the region of 650MΩ L-N, L-E and N-E.

as for the sockets, 2 chest freezers that are older then me are the cause of 50mA between them, rest is unnacounted for?

what causes this?
 
they were fine when they were using a map and compass, but now they've been supplied with a sat.nav. that's what's buggered the poor little sods. they want to take the neutral path, but the sat.nav. directs them down the earth path, even though it's clearly marked as " no through road for electrons".
 
the really confusing issue is when the positrons decide to intervene. a traffic jam at the junction would ensue, causing road rage and the release of megajoules of energy, this could result in a massive meltdown of the supply cable and so we could all have the rest of the day in the pub
 
use to be called a cell block, but now it's a custody suite with CCTV cameras in the bogs. wonder what the new name for a cess-pit is now. excrement suite? , poo parlour?
 
hi chr!s, care to expand on this?


Hi Pushrod

Well as Tel has already stated, becuae of the PME link the neutral current has a several paths, now dependent upon the CNE/PME impedance and the impedance of the protective conductors to earth, then you will find that some diverted neutral current will flow through the protective conductors.

The diverted neutral currents may be from your installation or even a neighboring installation.

Place a amp clamp around the live conductors at the origin on a TNC-S and see what leakage is present,and what the RCD will see.

Now dependent upon current, place a clamp/leakage clamp around the Earthing conductor and then other protective conductors.

See what you find:)
 
Oooh, now that's a tease. Are you suggesting that the imbalance in the live/neutral won't be reflected in the main earth for the instalation? That's nothing surprising because of the other extraneous paths, why is this more prevalent with PME? I feel like I'm missing something now ;)
 
i think the answer lies in a piece of toast. have you noticed, every time you drop a piece of toast, it always lands butter side down.
 

Reply to what causes earth leakage? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
969
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
645

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top