I am interested to know what else is wrong or if this is another EICR where it has no content bar the rcd issue.
 
I am interested to know what else is wrong or if this is another EICR where it has no content bar the rcd issue.
no earth continuity on 3 ccts
grommets missing from some spurs supplying heaters
some control equiptment not securely fixed
exposed copper in a spur unit
Inner cores of flex showing on entry into spurs
no ring con on neutral of a ring main

To name a few

The only grey area I'm not familiar with hence asking the question, is weather everything should now be covered by rcd as its twin and earth capped in the wall or just the ground floor sockets.
 
My point is that whether it was or wasn't required when it was installed has no bearing on how safe it is today. Therefore it isn't actually relevant to the observations you will be making about it.
I have started a conversation with you with a solar issue if you can help
 
My point is that whether it was or wasn't required when it was installed has no bearing on how safe it is today. Therefore it isn't actually relevant to the observations you will be making about it.
I have started a conversation with you with a solar issue if you can help
 
no earth continuity on 3 ccts
grommets missing from some spurs supplying heaters
some control equiptment not securely fixed
exposed copper in a spur unit
Inner cores of flex showing on entry into spurs
no ring con on neutral of a ring main

To name a few

The only grey area I'm not familiar with hence asking the question, is weather everything should now be covered by rcd as its twin and earth capped in the wall or just the ground floor sockets.
It states in BS7671 it should be given a minimum Code3 entry. This is minimum and other factors may warrant an alternative Code.
 
My point is that whether it was or wasn't required when it was installed has no bearing on how safe it is today. Therefore it isn't actually relevant to the observations you will be making about it.

Well of course it matters when it was installed, you are there assessing suitability for continued use, if it wasnt req when it was installed and all other test are fine then it should be a c3 which or you giving it a c2 and failing the whole install for ££££!! Your personal predrence shouldnt come into it. Now of course we both know rcd protection would be fantastic and i would also push to install rcd protection but the way your explaining it is poor advice to the op imo! It is an eicr not an new install.
 
Well of course it matters when it was installed, you are there assessing suitability for continued use, if it wasnt req when it was installed and all other test are fine then it should be a c3 which or you giving it a c2 and failing the whole install for ££££!!
Can you explain to me how the ommision of something would be more dangerous if installed at a time when it was required than it would be if installed at a time when it wasn't required?

Periodic inspection and testing is not to ascertain whether things were installed in a proper manner at the time they were installed. It is simply about assessing its suitability to remain in service, giving due regard to the Wiring Regulations as they now stand.
 
Phew I thought I was going to have to buy regulations 1 - 16 for a minute
LOL. Well following the logic of what is being claimed something installed to the 1st Edition should automatically be considered safe!

Of course that is a ridiculous position to hold!
 
If that regulation didnt exist when the installation was installed then your suggesting the whole install should fail even though all test show no damage or degrading to the circuit from when it was installed. So @Risteard you do an eicr tomorrow on a 16th edition board and all test results are exact the same to the day of install perfect good system and youll fail it for not having ams3 metal clad board and no 30mA rcd on lighting circuits with cables buried <50mm in plaster.? As an example.
 
If that regulation didnt exist when the installation was installed then your suggesting the whole install should fail even though all test show no damage or degrading to the circuit from when it was installed.

That would very much depend on the particular non-compliance with BS7671:2008 (2015) and its impact on the safety of the installation. Whether it was or was not required at the time of installation is completely and utterly irrelevant.

bigspark17 said:
So @Risteard you do an eicr tomorrow on a 16th edition board and all test results are exact the same to the day of install perfect good system and youll fail it for not having ams3 metal clad board and no 30mA rcd on lighting circuits with cables buried <50mm in plaster.? As an example.

An EICR does not "pass" or "fail" an installation - it assesses its suitability to remain in service. For example if I found a wiring system in an escape route with no fire resisting supports then I would judge that harshly irregardless of whether it was allowed at the time of installation or not, as it poses a danger to the fire brigade when entering the building.
 
Well of course it matters when it was installed, you are there assessing suitability for continued use, if it wasnt req when it was installed and all other test are fine then it should be a c3 which or you giving it a c2 and failing the whole install for ££££!! Your personal predrence shouldnt come into it. Now of course we both know rcd protection would be fantastic and i would also push to install rcd protection but the way your explaining it is poor advice to the op imo! It is an eicr not an new install.
There are some things which may not have mattered years ago which may well warrant a Code2 now.
 

Reply to what to suggest when no circuits have rcd protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
353
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top