Just had an interesting "discussion" with a fellow spark. Job was/is to replace a single lighting pendant in a first floor bathroom (loft above) with five IPX5 downlighters. Cables clipped to top side of 50mm roof trusses. Board only has RCD covering three ring mains and no spare way on this side of the board. Switch drop is between two sheets of plasterboard with a two inch gap and is not being modified.

RCBO or not for the amended lighting circuit?????

Regards
 
701.411.3.3: "Additional protection shall be provided for all low voltage circuits of the location, by the use of one or more RCDs having the characteristics specified in Regulation 415.1.1."
I don't really see that the Regulation is ambiguous, or can be interpreted other than as a requirement to provide RCD protection.
As the work proposed involves an alteration to the fixed wiring to a circuit of a location containing a bath or shower, in order for the alteration to comply, the whole circuit must be provided with RCD protection. Not just a part of the circuit by means of an RCD FCU.
 
Great debate and a few people shooting me down in flames (which I deserved).

The alternative for installing an rcd which I thought of from the start and no one has mentioned yet:-

From the original hard wired circuit, install a transformer able to supply all 5 lights and spider off to each. Selv has then been provided out of zones in the loft and no rcd is needed.

But of course we all would install a rcd because we all know its the safest way. Just liked the debate, that's all gents.

Can I take my tin hat off now? :)
 
I must admit there is quite a number of sparks think that if you do a minor works on an installation It can be to the same regs as when it was installed , no regulations change and the changes have to be brought in to existing installation and new so minor works to current regulations special locations also have to be notified , so this installation although minor would have to be done to current regulation so requiring an RCD
 
I must admit there is quite a number of sparks think that if you do a minor works on an installation It can be to the same regs as when it was installed , no regulations change and the changes have to be brought in to existing installation and new so minor works to current regulations special locations also have to be notified , so this installation although minor would have to be done to current regulation so requiring an RCD


Nice, so does this mean I can do CU installs on a MWC and not bother about bonding etc?? lol
 

Reply to What would you do? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top