Had a call out today, 12 flats no supply. Anyway ukpn tells me after they did their investigation that neutral becomes live when you put the cut out fuse back in so it is an internal issue. Would any of you disagree with their find findings?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss What's the problem? in the UK Electrical Forum area at ElectriciansForums.net
Hi Sparkie30
go to the begining you need to check you have a Nuetral coming into the building with all off, do ZE & PFC depending on your set TN supply or TT but I suspect TN-S or TNCS.
Establish this first could be a broken Nuetral outside or going down.
Then work away to main switch same thing, Ryefeild panel ECT.
Almost certainly a Nuetral going down or wrong polarity.
But start at the incoming supply make sure safe isolation also as you have a live Nuetral.
Should not not take long to prove incoming supply fault if it is.
Good luck
Well least it is sorted
they only needed one guy , a tester and a brain lol