Hi all,

As above really, just wondering the best Ze reading you've ever got on a TT system. Best i've found to date is 21 ohms.

Just how low is it possible to get? i'm intrigued...
 
Sorry dragging this thread up from the dead:) but today managed to get a reading of 0.51 on the earth rod for a garage only a 3/8in 1m rod into soft wet ground couldn't believe what i was seeing (tested with an earth loop impedance tester).
 
Test was done at earth rod in the pit just after it was driven in, there is no neutral earth fault within the installation, and the supply has just been commissioned by the LEB.
 
These extra low readings may be because of close proximity to a Tnc-s stake earth and commuting that way
The supply transformer earth resistance would account for greater readings

So a proper guiness book of records low TT reading is not awarded as far as I'm concerned :mad:
,thats because my best must be in the mid twenties only:(
 
Test was done at earth rod in the pit just after it was driven in, there is no neutral earth fault within the installation, and the supply has just been commissioned by the LEB.

If the test was done at the pit that's not a REAL Ze then is it? Mind you, I'm only jealous as my best is a mere 47 Ohms. I've had a Zs of 7 Ohms on a TT system before but alas that doesn't count either!

No Guinness Book of Records entry for me then....:(
 
0.51 ohms by pennywise? - sure you haven't driven the rod againsed the incomming supply cable or gas pipe? a colleague of mine did exactly that (near miss!). BTW, my best reading is 15.6 ohms
 
I am going to have to but in here and claim the all time record low for Ze on a TT system.

In Paris last week testing a new installation tested 0.14 ohms for a Ze on a TT (couldn't believe it).

The installation is a large office complex with a 3 phase TT supply. Main incomming cables are 240mm with 120mm main earth. This part of the installation was existing. After a lot of investigation as to the type of electrode used it was established that the 120mm main earth was conected to an earth plate buried in the courtyard of the building. From this plate a tape was run underground around the perimiter of the building and back to the earth plate in a ring.

Hope this gets me into the guinness book of records for lowest Ze on TT.
 

Reply to What's your lowest Ze recorded on a TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
695
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top