Just a few things i'm throwing out - Rings seem like they would be safer on 20A MCB but I guess there's very few accidents for this to be questioned by the powers that be.

If rings disappeared hypothetically would we loose the fused plug?

I'd be interested in the layout of some European Radials rules and Regs - Spider circuits and what's allowed.

This Hong Kong Code of Practice suggests Rings
I think a few other Asian countrys use them and wonder if they use Fused Plugs
Only just saw this post while searching for something else. But yes hypothetically you (and us) could lose the fused plug tops if we reduced the ring circuit to a 20 rather than 32 amp. Ironically in ROI we still use fused plug tops on 20 amp radials because rings are still allowed and an installation may be altered to incorporate a ring. On the continent I have never seen a fused plug top in use. All their appliances, come with unfused plug tops. If fused plug tops should disappear, they won't be missed.
 
But yes hypothetically you (and us) could lose the fused plug tops if we reduced the ring circuit to a 20 rather than 32 amp.
So long as all cables and accessories are rated for the fault.

To me having, say, a 3A HRC fuse on a smaller bit of electronics makes a whole lot more sense than trying to ensure everything (cable, connectors, switches, PCB tracks, etc) are able to safely clear a 20A MCB's let-through.

Lets face it, the majority of stuff is not in need of 10A supply, not even 1A in many case. Though the rest of the world either accepts higher fire risk or pays more for uprated conductors.
 
So long as all cables and accessories are rated for the fault.

To me having, say, a 3A HRC fuse on a smaller bit of electronics makes a whole lot more sense than trying to ensure everything (cable, connectors, switches, PCB tracks, etc) are able to safely clear a 20A MCB's let-through.

Lets face it, the majority of stuff is not in need of 10A supply, not even 1A in many case. Though the rest of the world either accepts higher fire risk or pays more for uprated conductors.
I think the waters get muddied sometimes regarding protection for appliances etc. Strictly speaking its the manufactures responsibility to ensure his product is adequately protected and is suitable to be plugged into the domestic installation its designed for. Electricians strictly speaking should only be concerned with protecting the wiring they are installing. Though we naturally are alert to any household accessories that we may feel merit a "closer look" Funnily enough the only times I have had concerns about cables been sufficiently rated for fault current and let -through has been in the control circuitry of appliances. In some traditional stand alone cookers for instance you could see 1.5mm and less supplying the rings and smaller again going to the controls. All backed up by a 32 amp mcb. Have never seen any of the cabling damaged by short-circuit though.
 
Electricians strictly speaking should only be concerned with protecting the wiring they are installing.
Indeed, but we are musing about the hypothetical case of different mains plugs/sockets being adopted in the a country that has the 13A fused ones already.

Realistically that is just not going to happen. It is like changing the side of road you drive on - the carnage and legal compensation trouble that would follow for years (or decades) is simply not worth it for whatever apparent rationalisation or consistency it might achieve. It has been done before, in the 60s with far fewer cars on the road, a bit like the change of UK sockets post WW2 with far less electrical goods in use - but it would be utter chaos now.

The issue is not one of how manufacturers make good safe - they can do so for equipment intended for EU, etc, but adequate cable cross-section for the flex length to manage the I2t aspect. Even if that is wasteful of the Earth's resources compared to lower per-socket fuses.

No, the issue now would be people cutting off 3A fused plugs from fused appliances that have 0.5mm cable for putting it on to a unfused plug on 20A MCB supply, or DIYers fitting some unfused sockets off a 32A ring or 40A cooker radial, etc. We know that should not be done, but it would be done in this scenario.

Of course then we would have to have £150 AFDD to get more safety that a couple of £0.30 fuses would have achieved...
 
Even if ring circuits were ripped out and replaced with radials, I can't think of a single reason that could be put forward as grounds for dispensing with fused plugs.

The only complaint I've ever heard is that they aren't particularly pleasing to the eye, but I don't remember ever looking at a plug from any another country and thinking it was a thing of beauty.
 
Even if ring circuits were ripped out and replaced with radials, I can't think of a single reason that could be put forward as grounds for dispensing with fused plugs..

The only complaint I've ever heard is that they aren't particularly pleasing to the eye, but I don't remember ever looking at a plug from any another country and thinking it was a thing of beauty.
Aside from the ascetics of other countries plugs (valid point by the way) I see little point in inserting fuses in circuits if they don't have a specific role. Having to pull a washing machine out from under a worktop or having to take apart the "chimney" in an extractor hood in order to replace a fuse in a plugtop are two instances I could mention where I would prefer the European method of an unfused plugtop on a 16 amp mcb.
 
Aside from the ascetics of other countries plugs (valid point by the way) I see little point in inserting fuses in circuits if they don't have a specific role. Having to pull a washing machine out from under a worktop or having to take apart the "chimney" in an extractor hood in order to replace a fuse in a plugtop are two instances I could mention where I would prefer the European method of an unfused plugtop on a 16 amp mcb.

Fair point, but how often do appliance fuses need to be replaced? Obviously an electrician would see more instances of this than an average householder, but they do receive remuneration for that service. Washing machines are indeed a pain to move - expecially where vinyl flooring is concerned, but extractor outlets could often be sited above wall units and in many instances this inconvenience stems more from poor planning during installation. In my own home I've replaced a handful of fuses over decades, but these were instances where I was making exploratory checks on a failed appliance - on none of those occasions had the fuse blown.

I don't think that electricians having to replace an occasional fuse is reason enough to undergo the huge upheaval that would be inolved in ridding these islands of fused plugs. I'd also question whether removing the relatively minor inconvenience of an occasional blown would come close to compensating for the potential issues caused by such a move?
 
Fair point, but how often do appliance fuses need to be replaced? Obviously an electrician would see more instances of this than an average householder, but they do receive remuneration for that service. Washing machines are indeed a pain to move - expecially where vinyl flooring is concerned, but extractor outlets could often be sited above wall units and in many instances this inconvenience stems more from poor planning during installation. In my own home I've replaced a handful of fuses over decades, but these were instances where I was making exploratory checks on a failed appliance - on none of those occasions had the fuse blown.

I don't think that electricians having to replace an occasional fuse is reason enough to undergo the huge upheaval that would be inolved in ridding these islands of fused plugs. I'd also question whether removing the relatively minor inconvenience of an occasional blown would come close to compensating for the potential issues caused by such a move?
I completely agree about the upheaval that may be caused as outlined by "Pc1966". And holding on to the fused plugtop is certainly no disadvantage. Considering that all fixed appliances now have isolators anyway (if inaccessible which they usually are) it would be very easy to arrange a SFU above the worktop and have literally an "unfused" plug top on the appliance itself. Problem solved.
 
I completely agree about the upheaval that may be caused as outlined by "Pc1966". And holding on to the fused plugtop is certainly no disadvantage. Considering that all fixed appliances now have isolators anyway (if inaccessible which they usually are) it would be very easy to arrange a SFU above the worktop and have literally an "unfused" plug top on the appliance itself. Problem solved.
Or simpler still, just have the 13A sockets above the appliance?

As above, when something blows a 13A fuse it is almost always a hard fault that is going to need the unit removed from its hiding hole for repair or replacement (OK, for 3A fuses and bedside lights then occasionally they would go with a filament lamp's bulb). If it were RCD sockets prone to random trips it would be very different, but I think I have only once had a fuse blow that upon replacing no other fault was found.

But I did not look inside for any remnants of an evaporated spider...
 
Last edited:
Or simpler still, just have the 13A sockets above the appliance?

As above, when something blows a 13A fuse it is almost always a hard fault that is going to need the unit removed from its hiding hole for repair or replacement (OK, for 3A fuses and bedside lights then occasionally they would go with a filament lamp's bulb). If it were RCD sockets prone to random trips it would be very different, but I think I have only once had a fuse blow that upon replacing no other fault was found.

But I did not look inside for any remnants of an evaporated spider...
Agreed. It's a very practical solution to have it about the appliance. But in a modern kitchen? Homeowners won't accept it
 
Appliances supplied with bare flex and connection plates fitted behind appliance would fulfil requirement for form and FCU above worktop providing function, although there'd be no end of complaints about the lost simplicity of a plugged connection.

I still don't see any practical issues with fused plugs hidden behind appliances, except where those appliances are integrated as that's just plain daft (although probably quite common).
 
rare to find enugh room behind an appliance for a plug and socket, unlees the woktop is the extra 2" wide.
 
Ah, the triumph of appearance over function! Could go in adjacent cupboards of course.
Yes. That is always my preferred solution. Issue there (in my experience at least) is that modern cupboards are now coming fitted out with all sorts of racking and specialised drawers meaning the socket is no longer accessible like we used to have with the old traditional cupboards. And inspectors are increasingly picky about what is and is, nt accessible. So to "avoid grey hairs" tend to stick to type
 

Reply to Why does the UK use rings for sockets? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
275
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
598
Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...
    • Like
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top