Why is split RCD not appropriate for TT? | Page 5 | on ElectriciansForums

Discuss Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It doesn't say that on the link you provided, either. So where are you getting the quote from?

The only rebuttal to what the regs clearly says has so far been something that's not in the regs at all. IMO it confuses things greatly. Could we stick to what's in the actual brown book instead of someone else's interpretation of it? Think it would help fuel the discussion instead of confusing matters.
 
It doesn't say that on the link you provided, either. So where are you getting the quote from?
Do you mean the

Provision may be made for isolation of a group of circuits by a common means, ?
 
With RCBO's the supply is via the busbar. It's in a fixed position so can't come into contact with the casing.
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
 
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
I can't find where it is and i haven't got the book, but it says:

“Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this”
 
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.

Things are starting to get a bit confusing, what quoted reg have I said isn't correct ?
 
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
The same could be said for a dual RCD board.
 
I can't find where it is and i haven't got the book, but it says:

“Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this”
It doesn't, i've searched an electronic version of the regs and that's not in there.

The reg i quoted was written verbatim from the book.
 
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.


I think that the cables feeding the rcds are the problem, not the busbars.


Regulation 531.3.5.3.2.201 requires that, where Class I enclosures are used (that is, earthed metalwork) on TT systems with RCD protection on outgoing circuits, all live conductors on the supply side of the RCD – that is, the internal cable links – must have double or reinforced insulation.


As each RCBO is supplied by a busbar, the risk of the busbar becoming loose and making contact with the metal enclosure is minimal.
 
It doesn't, i've searched an electronic version of the regs and that's not in there.

The reg i quoted was written verbatim from the book.


Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?
I only have the 17th edition green book to hand, but it's certainly in there.

537.2.1.2 : Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this
 
Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?
I only have the 17th edition green book to hand, but it's certainly in there.

537.2.1.2 : Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this
It appears to have moved in the 18th to 422.3.13:

422.3.13
Except as permitted by Regulation 461.2, every circuit shall be provided with a means of isolation from all live supply conductors by a linked switch or a linked circuit-breaker. NOTE: Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this.
 
It appears to have moved in the 18th to 422.3.13:

422.3.13
Except as permitted by Regulation 461.2, every circuit shall be provided with a means of isolation from all live supply conductors by a linked switch or a linked circuit-breaker. NOTE: Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this.
I stand corrected.

So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.

The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.

No wonder the rest of the world laughs at our electrical practices.
 
Last edited:
I stand corrected.

So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.

The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.

No wonder the rest of the world laughs at our electrical practices.

But if everything was as clear as glass, there wouldn't be forums like this where gentlemen discuss these things in a friendly, happy manner. 😇
 
Last edited:

Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
842
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top