Yes I did later I said 'suggested'.You said RCBO's were now required in residential installations.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes I did later I said 'suggested'.You said RCBO's were now required in residential installations.
Yes I did later I said 'suggested'.
And it should really say “Required”It does say 'shall be used'.
Thats what the thread was about why it's ok with rcbos and not ok using split rcds.NICEIC says you don't need a up front rcd
On TT main switch the rest of the board rcbo.
Where split consumer units are used with a separate double-pole main switch and 30 mA RCCBs to protect the final circuits, the interconnecting cables which connect the load side of the main switch to the supply side of the RCCBs must be provided with double or reinforced insulation to comply with Regulation 531.3.5.3.2.201.Thats what the thread was about why it's ok with rcbos and not ok using split rcds
Where split consumer units are used with a separate double-pole main switch and 30 mA RCCBs to protect the final circuits, the interconnecting cables which connect the load side of the main switch to the supply side of the RCCBs must be provided with double or reinforced insulation to comply with Regulation 531.3.5.3.2.201.
If this isn’t the case, this particular arrangement wouldn’t be suitable for TT installations because the interconnecting cables wouldn’t be provided with adequate fault protection. If the metal enclosure became live due to a fault, it would cause considerable inconvenience as RCCBs don’t have integral overcurrent protection.
A recommended consumer unit arrangement with RCBOs which is suitable for use on TT installations .
I have read the post, but some peapleMaybe a good time for you to read the complete thread, so as to avoid saying the same things
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.
It makes it compliant with regard to isolation
Every circuit that may have to be isolated without interrupting the supply to other circuitsevery circuit...that may have to be isolated without interrupting the supply to other circuits
should be provided with its own isolating device.
The device must switch all live conductors in a TT system
DP main switch meets requirement for swithcing of all live conductors. Perhaps I'm tired and unable to see what's in front of me, but how does this meet the requirement that every circuit be provided with "its own" isolating device?
That statement I think is the OSG interpretationevery circuit...that may have to be isolated without interrupting the supply to other circuits
should be provided with its own isolating device.
The device must switch all live conductors in a TT system
DP main switch meets requirement for swithcing of all live conductors. Perhaps I'm tired and unable to see what's in front of me, but how does this meet the requirement that every circuit be provided with "its own" isolating device?
Where are you getting this statement from? I've searched the regs and that wording isn't in there.That statement I think is the OSG interpretation
Isolation: 537.2
Every circuit / installation must be provided with a method of isolation from the supply. This isolation device should also be provided with a method to prevent unintentional or inadvertent reinstating (usually lockable).
In a TN-S or TN-C-S system it is not necessary to isolate / switch the neutral conductor providing that it is ‘reliably’ connected to Earth on the distributor's incoming supply side.
It’s worth remembering that semiconductor devices can not be used as isolating devices
“Provision may be made for isolation of a group of circuits by a common means”
Where are you getting this statement from? I've searched the regs and that wording isn't in there.