Why was the RCD test button not working?

HappyHippyDad

-
Esteemed
Arms
Supporter
Evening all...

I have just got back from a CU change. All was going very well and I was finishing early which was lovely for a friday evening, and then.......

The RCD on the opposite side to the lights trips when the lights are switched on... arghh. I eventually found the problem, I had screwed through the shower cable when attaching the CU to the piece of wood I was using to hang it on.

Whilst the screw was still through the shower cable (touching N-E) why did this stop the test button from working on the RCD? There was 240V going through the RCD and by using something on the other side of the dual RCD board it would trip, but it would not trip with the test button?

Cheers.
 
Ha, reminds me of panel wiring where the panel builder puts all the terminal blocks low down at the bottom of the panel. He can see to put his wires in the top side but FFS its near on impossible to "know" where the hole is for the outgoing, end up using the force and trial and error which leads to a bad back and me being grumpy for the rest of the day.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
telectrix,
Replies
19
Views
12,845

Advert

TrueNAS JBOD Storage Server

Back
Top