I live in Phnom Penh, Cambodia and people die here regularly by electrocution. There is no earth wiring in the buildings, just live and neutral.

I am a member of an expats forum and the question arises: Will using an RCD device offer any protection at all?
I understand RCD's will go off with any leakage and that may have to include the human being the earth. At the moment my apartment has 8/16/32 amp circuit breakers and nothing else.

I can buy plug-in type RCD units to go between an appliance (like the washing machine) and the wall socket. Will this offer any protection even it is me being the earth! 😱
 
It stopped flowing the moment you broke the circuit.
in the same way that the current (Amps) flowing through your lounge light stops flowing the moment you turn off the light switch.

ok, let me put it another way ---> why is an RCD unable to detect when a circuit is broken (with regards to my scenario)?

People say because the circuit is incomplete and or current has stopped flowing.......but so what......I still don't get why RCD's cannot recognise such an event?

I guess my point/question is not such much around 'why' it doesn't trip (I accept what you guys are saying in general) but moreso 'how' come it doesn't trip..........how can an electrical device such as an RCD, with our incredible modern technological advances and science and knowledge, not be able to detect when current stops flowing....seems hard to fathom that they can't be designed/programmed to handle such situations.

PS, I know I'm probably getting into some deep discussion here because of my ignorance, so apologies in advance.
 
.....how can an electrical device such as an RCD, with our incredible modern technological advances and science and knowledge, not be able to detect when current stops flowing...

The simplest reason is - that's not an RCD's job. The only job an RCD has is to compare the current in and current out through it's measurement coil. If IN=OUT then all is well. If not then trip.

There are absolutely devices who's job is to detect if current stops flowing. I've used them on heating elements to detect burnouts. But that application is specific. A device measuring current couldn't tell the difference between a broken wire and a switch being turned off, because all it sees is current or no current.

Regarding your earlier question about what 'happens to' the current already in the circuit when you break a wire / open a switch. Nothing 'happens' to it, it was never there. Current isn't something that fills up a wire like water in a pipe then has to either go somewhere or sit in place. The electrons are already in the wire, a flowing current just shuffles them around a bit and as soon as external voltage is removed they just stop. (Macroscopically, don't @ me physicists.)
 
So what happened to the 10A active in the circuit before the circuit was broken?
That’s returning down the N via the appliance so the circuit is balanced.

Remember that shorting the L to N should cause the fuse /mcb /rcbo to trip due to the high current and not the rcd as the circuit current would still be balanced.
 
Your scenario leaves out any earthing of the frame. So it's assumed the frame has no connection to earth or neutral. The live touching the frame doesn't complete any circuit, therefore there is no current flow for the RCD to measure. Therefore, all's right with the world from the perspective of the RCD.

got it....tx


Now along comes poor Joe, who is barefoot on a moist kitchen floor, and touches the live frame. Now some current flows through the RCD's coil.....

As in current starts to flow again because Joe touching the frame has created a circuit of sorts (with the earth)?
 
The simplest reason is - that's not an RCD's job. The only job an RCD has is to compare the current in and current out through it's measurement coil. If IN=OUT then all is well. If not then trip.

There are absolutely devices who's job is to detect if current stops flowing. I've used them on heating elements to detect burnouts. But that application is specific. A device measuring current couldn't tell the difference between a broken wire and a switch being turned off, because all it sees is current or no current.

Regarding your earlier question about what 'happens to' the current already in the circuit when you break a wire / open a switch. Nothing 'happens' to it, it was never there. Current isn't something that fills up a wire like water in a pipe then has to either go somewhere or sit in place. The electrons are already in the wire, a flowing current just shuffles them around a bit and as soon as external voltage is removed they just stop. (Macroscopically, don't @ me physicists.)

tx mate.....this was really helpful. Helps me better understand what's going on (and better comprehend previous replies from other posters).
 

Reply to Will an RCD offer any protection in a building with NO earth circuit? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top