Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.
Wasn't having a go mate,the whole Ra value thing is a lottery. As I've argued before,i just cant get my head around a view that pitches ANY high Ra value as 'better' than any other high Ra value.The end result will be the same whether it's 20 ohms or 1000 ohms. Tn values or you may as well go twiggy IMO lol.
You there Eng?
"In the mean time I will continue to go with 100 ohms purely because logic dictates its a safer bet than 200 ohms".
In context with the rest of the quote it seems logical to me !!
Where a TT system is used I will always attempt to get sub 100 ohm readings as opposed to 200 ohms because its a safer bet.
Is not the whole point to reduce the resistance of the earth return path to a point where stability issues are minimised.
Technically we can often go much higher than that, but I prefer not to always rely on what's technically correct.
Otherwise we can bring into play your own analogy of 1667 or even 1000 which I agree would lack logic, but on paper !!
BS 7671 are looking at values below 200 ohms.
NICEIC have quoted below 100 ohms, as does BS 7430.
Actually BS 7430 is a very interesting read so here's a link,
http://jack.nazwa.pl/doc/UK.17th/BS/BS 7430 Earthing.pdf
With reference to Skelts 200 mph vs 190 mph,
If its a Ferrari, with decent brakes, on a traffic free autobahn !!
GO FOR IT unk:
Wasn't having a go mate,the whole Ra value thing is a lottery. As I've argued before,i just cant get my head around a view that pitches ANY high Ra value as 'better' than any other high Ra value.The end result will be the same whether it's 20 ohms or 1000 ohms. Tn values or you may as well go twiggy IMO lol.
You there Eng?