Are you sure the circuits are labeled correctly???

i.e you linked r1+r2 at DB circuit labeled flat1, testing at flat 1 but the r1+r2 circuit is actually flat 4?

Thats a good suggestion. More like the type of thinking I was talking about
 
I have returned to the thread chaps sorry about the long time away,I should have updated this ages ago apologies all round.
Right long story short went back a few days later, long wandering extension lead in hand, found out it was exactly what VMAN suggested the D.B was incorrectly labelled apart from flat 5, so when I thought I was doing r1+r2 on flat 1 it was actually flat 3 as labelled on the board.
thanks to everyone who posted for your help and suggestions
nice on lads
(don't worry in future I will report back straight away)
 

Reply to Zdb ok but no R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
808
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
984

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
947
  • Question
if the 3 spaces with charge points are always allocated to the same 3 flats, surely the easiest way is to run the supply to the load side of the...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top