Ze external earth loop impedance
better watch it, geordie, she'll be running off with a cockney next.
And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.
Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V
250-35 = 215 V, very close to the 216.2 V minimum(230-6%)
Eh???? I think you need to have a think about that.
Also, with a TN supply, if yar Ze is too high, an Earth fault won't take out the intake fuse. (depending on A rating)
Just in case I'm misunderstanding you...walk through it once more.
Well on a single phase system whats the mimimum voltage.
So for a 100 amp supply, assuming a current of 100amps 35 volts will be dropped in the supply.
So if at Tx terminals we have 250v then and 35 v dropped across supply then only 215 v is supplied at the consumers service head