So how far do you go with requesting the isolation of an installation to carry out a Ze with the removal of the main earthing conductor? Days, weeks, months? Do you sacrifice clients and refuse work purely because you cannot disconnect the main earthing conductor?
It's not short cutting and inspectors are not 'cowboys'. GN3 clearly states limitations are at client and inspectors discretions. I for one have never isolated one of our clients (hospital) installations to carry out a Ze by removal of the MEC.
 
If it's an agreed limitation Paul that's fine, no one would turn power off in a hospital with out a shed load of forward planning. Too many people at risk and I certainly don't want someone's death on my conscience. In a domestic though there is no excuse for not doing it properly.
 
If it's an agreed limitation Paul that's fine, no one would turn power off in a hospital with out a shed load of forward planning. Too many people at risk and I certainly don't want someone's death on my conscience. In a domestic though there is no excuse for not doing it properly.

That's it perfect can't agree more done cases it's not possible but for smaller installations no excuses
 
So how far do you go with requesting the isolation of an installation to carry out a Ze with the removal of the main earthing conductor? Days, weeks, months? Do you sacrifice clients and refuse work purely because you cannot disconnect the main earthing conductor?
It's not short cutting and inspectors are not 'cowboys'. GN3 clearly states limitations are at client and inspectors discretions. I for one have never isolated one of our clients (hospital) installations to carry out a Ze by removal of the MEC.
You have misinterpreted my response and i have already stated its tailored for the OP's domestic situe where simply been lazy and not doing it is cowboyish... i furthed this by noting that it is not always an option but expressed these are bigger installs commercial and industrial.... agree 'shortcut' probably the wrong word but it is in a sense that it saves a power down, time, money and inconvenience and yes is in the bigger world acceptable.

As i said i have also left earth connected in hospitals.

Having said that we had to get permissions to test this way from the site Electrical design engineer as this was not our call.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ze
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
25

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Buzz-light-bulb,
Last reply from
Brightspark2,
Replies
25
Views
2,940

Advert

TrueNAS JBOD Storage Server

Back
Top