2C 16mm SWA should be 1.15 mOhm/m for R1 and 3.7mOhm/m for R2, so R1+R2 ought to be around 0.49 ohms. as @SJD says what you are seeing is a lot higher than realistically expected here so look for loose/corroded glands at the ends, or missing banjo+flying leads so it is depending on rusty/painted enclosures for the CPC.

If both ends are good and clean then it points to a more worrying aspect that it could be corroded armour underground somewhere, but that would usually take years to develop following puncture of the surrounding sheath. Also IR the cable on its own (both ends disconnected and wiped clean of any dust/damp), that might indicate water ingress somewhere if it looks low-ish.

More generally you won't get much of an improvement with an earth rod, often it is hard to get Ra below 50 ohm with most soils and that is not going to make a significant change to 2.4 ohms.

If after fixing it still is too high for the supply OCPD then fitting a delay RCD along with the MCB/fuse feeding it is another means of ensuring ADS times are mot and you still have a sporting chance of selectivity with end circuit RCD/RCBO at the annex CU.

You could use a rod and delay RCD if the armour is failing and cable otherwise OK, in effect making the annex a TT system with part of the sub-main on TN earthing (to the corroded segment) and the end of the system on TT using the rod at the annex. But you have to be able to meet ADS on the rod alone, hence the only realistic option is a 100mA or 300mA delay RCD as part of the supply protection.
 
 
Sounds a bit high a reading to be due to just the cable resistance? What is Ze at the supply origin? Perhaps poor or corroded connections of the armour?
Connections look all clean and tight with origin reading 0.16
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great
Sounds a bit high a reading to be due to just the cable resistance? What is Ze at the supply origin? Perhaps poor or corroded connections of the armour?
 
So should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?

I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
 
Didn't you get an IR reading of 0.7M between two of the conductors?
I did. Have since gone back withnewly calibrated tester and done a new clean test. Its quite concerning that the reading is so different. The 63a mcb at origin has tripped out several times but not recently.
 
So should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?

I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
cable in ground approx 25 years
 
Do some continuity tests to establish where continuity is amiss.
R1+R2, R1+Rn, R2+Rn.
 
Last edited:
Ze o
Connections look all clean and tight with origin reading 0.16
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great


You don't appear to be clear with the problems here.

You talk about insulation resistance of 2.36 to 4.27 - is this Mohm?

This is irrelevant to the Zs

You don't appear to know the differences between insulation resistance, Ze and Zs.

If you do have Ze of 0.16 ohm at the feed end of the cable and ~2.5 ohm at the load end, there is absolutely something wrong with the cable or terminations.

I would expect a r1 + r2 of 0.5 ohms or thereabouts.

You need to find this fault, not cover it up by adding rods or anything else.

You need to measure the r1 + r2, the r1 + rn etc. This will show if you have a cable fault. And will identify which conductor is the problem, if they all read 0.5 ohms (less for r1 + rn) then the fault is between the cable feed end and the header. - most likely a bad connection in the earth path.
 

Reply to Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
850
Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
394

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock