Zs a little out, what can I do to fix it? | on ElectriciansForums
Discuss Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net
I
Inteificio
Hi.
Am working in a factory, most of the machinery on the main floor is fed from are fed from spurs (2/3 machines per spur).
As they have all been fitted with D type breakers, we need a tight Zs.
We have not got it.
I am trying to think of the easiest way of fixing it.
Turns out I'm not 100% sure what you can do with CPCs.
If each circuit has it's own dedicated CPC, can I also link a supplementary CPC (or even make a link between each CPC to have a star supplementary earth in addition to the original?)
I've flicked through the regs and can't find any info on supplementary earths!
The way I read it, is as long as all the CPCs are in the same enclosure you can do what you want!
Anyone with a bit more experience got a few tips?
Thanks,
Sorry for not giving more details.
Existing circuit that seems to be thrown together from spare parts.
Break size from 20 up to 32.
Zdb a rather nice 0.09
I have done most investigation on 1 circuit as I got a shock off it (from touching the chassis!!!)
D20 Zs 1.18
All circuits are feeding a selection of 3phase 16/32, single phase 16/13. Equipment is moved around room a lot so load varies.
Basically it is a mess, hence why I need help!
I would run supplementary bonding to any nearby steelwork, and also common the CPCs to the machinery, by Bonding them all to Common steelwork. It's in our contract specifications to do this, but I think it's good practice, and doesn't take long. Even linking nearby containment together can reduce Zs.
on our jobs we have to link any glands to the containment that feeds it, and also the chassis of any equipment, to maintain an equipotential zone.
Reply to Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
4K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...