I

Inteificio

Hi.

Am working in a factory, most of the machinery on the main floor is fed from are fed from spurs (2/3 machines per spur).

As they have all been fitted with D type breakers, we need a tight Zs.
We have not got it.

I am trying to think of the easiest way of fixing it.
Turns out I'm not 100% sure what you can do with CPCs.

If each circuit has it's own dedicated CPC, can I also link a supplementary CPC (or even make a link between each CPC to have a star supplementary earth in addition to the original?)
I've flicked through the regs and can't find any info on supplementary earths!

The way I read it, is as long as all the CPCs are in the same enclosure you can do what you want!

Anyone with a bit more experience got a few tips?

Thanks,
 
Sorry for not giving more details.
Existing circuit that seems to be thrown together from spare parts.
Break size from 20 up to 32.
Zdb a rather nice 0.09

I have done most investigation on 1 circuit as I got a shock off it (from touching the chassis!!!)

D20 Zs 1.18

All circuits are feeding a selection of 3phase 16/32, single phase 16/13. Equipment is moved around room a lot so load varies.

Basically it is a mess, hence why I need help!
 
I would run supplementary bonding to any nearby steelwork, and also common the CPCs to the machinery, by Bonding them all to Common steelwork. It's in our contract specifications to do this, but I think it's good practice, and doesn't take long. Even linking nearby containment together can reduce Zs.
on our jobs we have to link any glands to the containment that feeds it, and also the chassis of any equipment, to maintain an equipotential zone.
 

Reply to Zs a little out, what can I do to fix it? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top