if you have the ze and know the length of a circuit can you calculate the zs ?
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs and circuit length in the UK Electrical Forum area at ElectriciansForums.net
if you have the ze and know the length of a circuit can you calculate the zs ?
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
How would you do it I guess because when know the resistance of the cableYes.
How would you do it I guess because when know the resistance of the cable
if you have the ze and know the length of a circuit can you calculate the zs ?
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
Will the zs be lower or higher or does it depend?You can predict the Zs by calculation, but this will not necessarily be the actual Zs of teh circuit.
You can look up the R1+R2 per metre from data sheets to calculate the predicted R1+R2 then add this to the Ze to predict Zs.
This is an important step in the process of designing a circuit.
Will the zs be lower or higher or does it depend?
So for example how would I work out the calculated zs of 1.5/1 twin at 100m with a ze of 0.24
Find 1.5mm/1mm in that table times it by 100 then add the ze to it
Will the zs be lower or higher or does it depend?
So for example how would I work out the calculated zs of 1.5/1 twin at 100m with a ze of 0.24
Find 1.5mm/1mm in that table times it by 100 then add the ze to it
Yes, but more for design I'd say.You should also do this calculation before testing, so you can confirm that the measured value is as expected
Yes, although given an unfamiliar circuit, I would calculate an expected r1+r2 when measuring it, even if it is within the max Zs of the protection, as if it calculates at 1 ohm, but measures 1.9 (still within the 2.2 of protection) there is still something wrong- perhaps loose connection.Yes, but more for design I'd say.
Yes, we're talking basic stuff.Yes, although given an unfamiliar circuit, I would calculate an expected r1+r2 when measuring it, even if it is within the max Zs of the protection, as if it calculates at 1 ohm, but measures 1.9 (still within the 2.2 of protection) there is still something wrong- perhaps loose connection.
But yes bread and butter calculations at the design stage
Zs might be lower, but it really depends on the type of system.So if my circuit was 100 meter it would be :
1.5/1 mm cable is 30.20 /1000= 0.0302
0.0302x100= 3.02 + ze would equal zs but the zs should be lower than that due to parallel paths to earth?
Zs might be lower, but it really depends on the type of system.
Usually you find the DB Zs is a bit lower than the supply Ze because of bonding to gas/water pipes, etc, providing parallel earth paths. In your case if Ze went from 0.24 ohm to, say, 0.1 ohm it would make very little difference to the Zs for the 1.5mm circuit as you are adding 3.02 to it. So it has (3.02 + 0.24) / (3.02 + 0.1) = 1.045 (so under 5% change).
What can make a difference is if it is in something like an industrial situation feeding floodlight or similar on a steel structure that are earthed and you have that path in parallel to the T&E's internal 1mm CPC. Then you might see an ohm or so less and that is a significant change in your Zs.
But from a design point of view you should not assume such parallel paths are there, they might not be in the future if something changes (e.g. metal water pipe is replaced by plastic), so you should be designing for sufficiently fast & safe disconnection on a fault from the installed cable & DB value of Zs
That might be a solution, but generally there is only a small range of cases (i.e. cable length & OCPD rating, etc) when you fail to disconnect on Zs but still are OK for voltage drop. You should check that as well before deciding to go up a cable size or take some other action.Cheers man
So if the circuit after all that doesn't meet zs does it comply if put on an rcd or rcbo