if you have the ze and know the length of a circuit can you calculate the zs ?
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
Ze : 0.24
Circuit length : 100m
1.5mm cable twin
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Zs and circuit length in the UK Electrical Forum area at ElectriciansForums.net
So if your voltage drop was complaint but your zs was not using a rcd or rcbo would make the circuit comply?That might be a solution, but generally there is only a small range of cases (i.e. cable length & OCPD rating, etc) when you fail to disconnect on Zs but still are OK for voltage drop. You should check that as well before deciding to go up a cable size or take some other action.
You would not do it for 1.5mm T&E, but for bigger SWA you might find the most cost-effective option is to run a separate copper CPC in parallel with the SWA armour to get R2 down far enough.
Yes, it would then comply.So if your voltage drop was complaint but your zs was not using a rcd or rcbo would make the circuit comply?
It is not bad design as such.But I'm guessing that would be bad design but still complaint....:/? Of so why would it be done like that would it be down to cost or lack of a better option?
My dude you are a legend real, the above is like a college lesson.Yes, it would then comply.
The quickest way to determine what is going to be OK is to look at the IET's On-Site Guide in Table 7.1(i) that lists the most common combinations of cable and over-current protection for:
In the columns for max length if has 'typical' cases for Ze for TN-S and TN-C-S cases, and with/without RCD protection. It also tells you what is limiting the length where they vary (e.g. volt drop, Zs, or not permitted as adiabatic limits exceeded, etc).
- Ring final circuit (5% drop, loads distributed)
- Lighting radial circuit (3% drop, loads distributed)
- General radial (5% drop, load at end of circuit)
It also advises on the typical "installation methods" that are acceptable, but does not cover other thermal derating requirements due to bundled cables or hot zones. You need to consider them separately in the design stage.
It is not bad design as such.
But it is not the best design as you then depend on the RCD electronics to protect against even a hard fault (not just direct-contact electric shock) and the reality is in most cases folk do not periodically test RCDs. Even though CU are polluted with labels for all sorts of pointless things including this one important aspect!
The thermal/magnetic trip of the MCB side of a RCBO (or in series with a RCD) is much simpler and more reliable, but depends on Zs being low enough.
So my own advice would be in cases such as this you need to look at the risks and justify if a single RCD is an acceptable trade off.
Where it is likely is something like a small fixed load in a remote location, say a couple of floodlights, where the design current is only, say, 1-2A and thus a long run of 1.5mm or so is perfectly OK, but then Zs is too high for your usual 6A B-curve MCB or similar. You can then look at:
- Is the circuit high risk? If it is run well out of normal reach then the consequences of a failed RCD are less of an issue than if it is, say, a floodlight fixed on something like a hand railing, etc.
- Can I fit a smaller MCB? If you are using RCBO, and for many domestic CU choices, then 6A B-curve is the smallest (in the sense of highest Zs), but for TPN style boards for commercial/industrial you may get MCB down to 2A C-curve (with Zs requierment equivalent to a 4A B-curve) or less. E.g. Hager go down to 0.5A C-curve for the likes of a bell transformer, etc.
- Should I use a bigger cable? Going from 1.5mm to 2.5mm might not add too much cost anyway, but if you are going from 25mm SWA to 50mm it is a serious consideration for cost and wrangling!
- Dual RCD if high risk or TT? Having a 100mA or 300mA delay RCD as the DB incomer means you have selectivity with a working 30mA RCD/RCBO, but should it fail the incomer will disconnect everything. Yes, there is a risk there, but if significant then you ought to have emergency lighting, etc anyway as power can go off for reasons other than your 1.5mm & related RCBO circuit failing!
Thanks, hope it helps!My dude you are a legend real, the above is like a college lesson.
Also depends on the risks. You can't normally "grab" a light switch so the risk of injury from shock is only high if you could also be well grounded at the time. Are there other metal objects the operator could simultaneously touch? Is it a wet zone or outdoors?So what if its out of reach like a light and a class 2 fitting then its not high risk...
But a metal fitting light switch is...
For any device (MCB, fuse, MCCB, etc) if you look at the manufacturer's data it will show curves of time and current. You look along the time = 0.4s axis and see what (maximum) curve is that hits that, and down to find current is needed to reach there. Then you compute the Zs from:The fact you can go lower than 6 amp mcb is pretty cool that means you can use longer circuit lengths and still meet VD and or zs more easily but how would you find the max zs of breakers lower than 6 amps?
So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cableOne final thing to consider for unusually long cables are:
They are both a warning signs that you need to consider the design in far more detail.
- If you are failing to meet the Zs for MCB disconnections times, or
- If you fail to meet 5% voltage drop at the MCB rating (even if it is OK at the fixed load's current that you intended)
Basically you might use an RCD to mitigate the high Zs situation, but you also have to consider the risk of a L-N fault also failing to disconnect quickly (as that is not considered a fault by the RCD). So you need to make sure that the over-current aspect (i.e. MCB) will prevent a fire if the cable is overloaded for a long time due to a end-of-line short not resulting in enough current to trip the MCB quickly.
That is the simplest / easiest option to avoid much more analysis. If the cable is already in then looking at a smaller MCB (if available for the distribution board) would be the simplest approach.So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cable
But what would count as an overly long circuit?That is the simplest / easiest option to avoid much more analysis. If the cable is already in then looking at a smaller MCB (if available for the distribution board) would be the simplest approach.
If designing from scratch then looking at "6A B-curve" as readily available and usually in the van as a spare would point to using a bigger cable, as here going from 1.5mm to 2.5mm is not a big cost factor.
One where Zs or VD on the chosen cable CSA, length, and MCB are not being met!But what would count as an overly long circuit?
100m? 150m?
So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cable