This is an old house - 1930s onwards.
Doing my first certificate and have a question on my Zs Reading on a ring circuit on a type B 32A MCB BS 60898.
The measured Zs is 1.21 (my R1+R2 reading is 1.27) and the RCD trips at 43.6ms. (5x =13.9ms)
Now table 2D in the OSG says the max Zs allowed is 1.16 ohms and I know I should be looking at a trip time of less than 40ms.
Is this actually acceptable or do you have any suggestions on how I can get the Zs down?
The house is a standard detached house, not massive and this is on the downstairs ring circuit.
On a seperate note, the upstairs ring has a broken neutral and short of lifting all the floors in each room (which the customer deos not want me to do), I have no idea where it could be - the socket connections are fine but there are some spurs. I have connected this ring to a 16amp MCB, treating it as a radial circuit. Is this ok?
Thanks, Dicky
Doing my first certificate and have a question on my Zs Reading on a ring circuit on a type B 32A MCB BS 60898.
The measured Zs is 1.21 (my R1+R2 reading is 1.27) and the RCD trips at 43.6ms. (5x =13.9ms)
Now table 2D in the OSG says the max Zs allowed is 1.16 ohms and I know I should be looking at a trip time of less than 40ms.
Is this actually acceptable or do you have any suggestions on how I can get the Zs down?
The house is a standard detached house, not massive and this is on the downstairs ring circuit.
On a seperate note, the upstairs ring has a broken neutral and short of lifting all the floors in each room (which the customer deos not want me to do), I have no idea where it could be - the socket connections are fine but there are some spurs. I have connected this ring to a 16amp MCB, treating it as a radial circuit. Is this ok?
Thanks, Dicky