And if an rcd is used , in this case a 100mA in doesn't mater if your zs is 356 ohms
Hey fella, have a read of note 2 411.5.2, that will help you and may clear things up. Regards.And if an rcd is used , in this case a 100mA in doesn't mater if your zs is 356 ohms
it would exceed the maximum earth fault loop impedance as table 41.5 for a 100MA which is 500 Ohms, that said any reading above 200 ohms should be considered unstable 542.2.4How about if it's 3560 ohms?
Note 2 again?No glen not have a good go, no no no , support what I am saying.
if you have ze of 14 ohms what is the point of doing zs test , as you know your readings are to high for protective device already.
Brains just ain't your friend last two days guys , AAA?