Ahhh Hawkmoon the eternal champion....the old "you might of damaged or pulled out a conductor" argument. But what if it was a radial with a FCU on the end? Wouldn't you have to take it off the wall to measure Zs?
I know Zs is the whole circuit or loop impedance path, read post No 58..oh here it is
"Agreed, I like to test it myself too, but an Ra plus R1+R2 of each final circuit will give a more accurate/stable assessment of the earth fault loop impedance and would not include parallel paths which may be removed at some point.
I've had Zs values on TT installs that fall easily within the TN bracket and would suggest that an RCD would not be required to meet disconnection times, but if these parallel paths were to be removed then obviously the tiny earth fault currents would not disconnect at any time. So how significant is a measured Zs in this instance?
Remembering Im talking about RCD protected TT install here