Robbo

-
Joined
Mar 23, 2019
Messages
12
Reaction score
1
Location
Northwest
Doing some prior tests befor installing a fused spur from a radial circuit, and have found the Zs reading higher then the current regs, obviously it complys with a past reg, but as I’ll be doing a minor works for the job, when filling out their cert would I just put it down as an observation in comments on current installation and grade it C3.

Cheers.
 
Just though, could it be argued that the Zs you're interested in is that relating to the fuse in the FCU, which for a 13A BS1362 is 1.8ohms for a 0.4 second disconnection time..

Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.
 
Reading is 0.79 at the furthest point, like I said it’s the only socket on the circuit, and is about 10-15mtr run from its DB

Hi,

You say it's a radial & that it is the only socket on the circuit & that Zs is 0.79

Yes a 30mA RCBO max is 1667 ohms


Just out of interest what csa is used on the radial? because if it's in 2.5mm on a 32A RCBO then the OCPD is to high for the cable ie. highest is 27A on clipped direct for t&e.

ie. an A2 radial is 4mm on a 30/32 amp OCPD, Zs stated in BBB for type C is 0.68 ohms (4mm is what I'm assuming is used on your radial)

An A3 radial is in 2.5mm on a 20 amp OCPD, Zs stated in BBB for type C is 1.09 ohms
So a 20A type C RCBO Zs at 80% is 0.872 ohms
 
Last edited:
Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.
That's why I like this game, and this forum.

You have to think as often there are many answers that will work, some unnecessary solutions and sometimes it's fine as it is.
 
What about fault protection up to the spur.

Fair point, I had it in my head that spur origin was back to back, or side by side with the FCU in the same CSA cable as the original circuit. Then the new run to a DP isolator for the stair lift. In this I wouldn't be losing a great deal of sleep.

However it could equally be spurred, 10m cable run with FCU at the end, in which case you're right.

Any case it's on an RCBO so who cares, apparently.
 
Using 1667 as a get out for poor design doesn’t sit right with me.

As asked before what rating is the RCBO, nearest C type is 32 amp at 0.68. What CSA is the cable and what is Ze and earthing arrangement?
 
In this case then due to bad design/change in Regs the high Zs is through no fault of yours.

In this case I would utilise the RCBO for fault protection although. This is not permitted in Bs7671 so will need to be recorded on the MWC as a deviation.
 

Reply to Zs reading does not meet current regs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top