Tony has a valid point, ...Hes referring to pic #3, ...Plastic ties won't hold these cables in place on the occurrence of a heavy fault!! Cables carrying heavy fault current act like a fireman's hose under pressure, without a fireman or two holding it in place.

Generally, on panels where heavy cables are passing through a cable cabinet to a connection point a means of bracing those cables should be provided...

If you look at pic #2, you will see an example of bus bar bracing!! All panel bracing is designed to cope with the KA rating of the panel. If this is a 1MVA Gen-set, probably around 20 to 25KA
 
Last edited by a moderator:
Good points made by everybody concerned. I'll bear them in mind for future works. Never even considered the tie wrap scenario
Would the same happen with 4-c SWA? Generally you see them just tie-wrapped to the ladder racking, tray, ect.
 
Good points made by everybody concerned. I'll bear them in mind for future works. Never even considered the tie wrap scenario
Would the same happen with 4-c SWA? Generally you see them just tie-wrapped to the ladder racking, tray, ect.

Under extreme fault conditions a SWA can be blown apart. But that would really be worse case scenario.
When singles are used then magnetic repulsion is a real danger. I’ve actually watched bus-bars bending under the start up load of a squirrel cage motor. That came about because a MCC panel had been extended several times without due consideration to the overall effect on the bars. “It’s only a 100HP motor, it’ll be OK.” The trouble was several “it’s only” situations that had happened over the years. To the point where the bars gave up the ghost, bent and shorted out.
 
Under extreme fault conditions a SWA can be blown apart. But that would really be worse case scenario.
When singles are used then magnetic repulsion is a real danger. I’ve actually watched bus-bars bending under the start up load of a squirrel cage motor. That came about because a MCC panel had been extended several times without due consideration to the overall effect on the bars. “It’s only a 100HP motor, it’ll be OK.” The trouble was several “it’s only” situations that had happened over the years. To the point where the bars gave up the ghost, bent and shorted out.


I've only ever seen the results of a catastrophic fault on a dual supplied 3200A LV switchboard!! Where the bracing supplied by the manufacturer, was found to be, not up to the fault KA rating of the board. Which should have been 50KA but was in fact, barely reaching 32KA bracing levels. Two complete panel sections needed to be totally replaced and bracing upgraded throughout the entire switch board!! A very expensive exercise for the manufacture, which was only mitigated to a small degree by a wrong doing of the contractor who also ended up paying a pretty price!! lol!!

NOT one of my projects i should hasten to add!! lol!!
 
Looks like we're dealing with large forces here...

A three-phase short circuit in trefoil formation, the maximum force on the
conductor as detailed in IEC 61914:2009 (Appendix B Equation B.6), is
described by the following:

F[SUB]t[/SUB] = (0.17 x i[SUB]p[/SUB][SUP]2[/SUP])/S

Where
F[SUB]t[/SUB] = Maximum Force per unit length of cable (N/m)
i[SUB]p[/SUB]= Peak short circuit current (kA)
S = Centre-to-centre distance between neighboring conductors (m)

when the currents are in 100s of kA!!!



Interesting stuff!
 
Looks like we're dealing with large forces here...

A three-phase short circuit in trefoil formation, the maximum force on the
conductor as detailed in IEC 61914:2009 (Appendix B Equation B.6), is
described by the following:

F[SUB]t[/SUB] = (0.17 x i[SUB]p[/SUB][SUP]2[/SUP])/S

Where
F[SUB]t[/SUB] = Maximum Force per unit length of cable (N/m)
i[SUB]p[/SUB]= Peak short circuit current (kA)
S = Centre-to-centre distance between neighboring conductors (m)

when the currents are in 100s of kA!!!



Interesting stuff!

Fault currents are limited by what the transformer in question can deliver into a fault!! Obviously the larger the Transformers KVA/MVA rating, the more current it can deliver into a fault!! For a typical 240/415V 1000KVA transformer, is roughly about 20KA...
 
So Ip is only 400,000,000 (20K²). That’s OK then :ack2:

It gets worse the more you look at it.

So if we allow 50mm conductor centers:

Ft = (0.17*(20K²))/20 = 3,400,000 N/m

A nylon strap’s going to hold that, isn’t it?
 
Last edited by a moderator:
Is this force only generated between conductors carrying different phases, or does it happen in single phase cables too? I'm wondering if this effect happens in, say, your domestic T&E to a lesser extent with the lower fault current.
 
To be honest in final circuits, the fault current is very low so although there will of course be repulsion, it will not be anywhere near the levels of the forces generated at the origins of larger industrial installations. Use Archie's formula to try the numbers for yourself. You could transpose it to see what fault current you would need to cause a certain force.
 
OK assume a fault current of 0.5KA on a 2.5 T+E, I get 127 N/m. It's not going to do it a lot of good.

To put this in to context under a load of 20A the 2.5MM T+E has got 0.2M/m of force acting within it.
 
OK assume a fault current of 0.5KA on a 2.5 T+E, I get 127 N/m. It's not going to do it a lot of good.

To put this in to context under a load of 20A the 2.5MM T+E has got 0.2M/m of force acting within it.

That would explain why cables blow themselves to pieces.
It's all starting to make sense now!
 
Last edited by a moderator:
The bars I watched bending were within 20m of the 1000KVA transformer. Don't know what current they were carrying at the time but couln't have been much above 1500A It was a 100HP DOL motor starting on an already loaded board. Normal running would be about 1100A The board was a Metro Vick open slate panel.
 
Never seen bars actually bending, a sight to see that i bet!! lol!!


I have seen package sub-stations (MV/LV) that have come from the factory with next to no bracing on the 3 phase bars entering the LV panel. That was after a factory visit (GE) too, ...where the units that were up for delivery to site were inspected and witness tested by myself!! Those 3 units were fine, but the next 4 units were crap, (12 X 1MVA units in all on that project) and after opening the first unit, instructed the contractor to send them back for remedial work, which both the contractor and myself will inspect at the factory, before they are shipped back to site!! That was in Saudi, but the factory was run and operated by GE (USA) at the time!!
 
The Metro Vic panel was from the late 40's, all open at the back. I was the wet behind the ears idiot that got talked in to watching what was happening.

After talking to Archy we’ve revised the figures for the 20KA calculation (I used A and not KA) the new value of F = 1360N/m. Not as bad as it was, but it’s going to throw things about violently if the cables get loose. The last transformer install I did I used 3.5T of cable on the secondary side. I wouldn’t fancy getting clobbered by that lot.
As Archy said the film of the multi-core cable exploding says it all.
 
That would explain why cables blow themselves to pieces.
It's all starting to make sense now!


Many factors involved, depends on the cable size, (they also have a KA/s withhold rating too) length of cable etc. More chance on a short length of cable, say between TX and Main Switchboard, than on a long run (depending where the fault occurs), as the cable will act as resistance/impedance, limiting the fault current the transformer can deliver into the fault...

As i say too many factors involved that can/will influence each other, to pick-up on just one aspect and predict what will happen under a given fault condition.
Safe to say, any fault that involves the full fault current of a transformer, will always be catastrophic, ...and expensive!! lol!!
 
Engineer 54 you are obviously very knowledgeable but I've never seen you post any pics of your work up, come on I think it's time to show us lol


Should have asked a couple of weeks ago. Not that i have much in the way of past project photo's anyway!! What i do have are on the PC, and it's too late getting that out of mothballs now, as i'm off flying back tomorrow!! So you'll have to wait till the summer now!! lol!!
 
Rewire sorting this mess out. Will post drawings and other stuff gradually as I do them
 

Attachments

  • image.jpg
    133.8 KB · Views: 707
Rough and missing terminal numbers, just rough copies before a proper computer drawing neat and standardised. Pretty basic circuit as you can see but I thought I'd share

This is just a control panel for a Plasma Nitrider. The complicated side of this machine is all in an Electronic Circuit (which I have the drawings for if anyone is interested) it's packed full of inverters and rectifiers. The more complicated stuff comes with the Arc Detection parameters. My company had a Romanian Physicist custom make it for us, he apparently works on the LHC now lol.
 

Attachments

  • image.jpg
    109.1 KB · Views: 180
  • image.jpg
    135 KB · Views: 144
  • image.jpg
    150.6 KB · Views: 145
Last edited by a moderator:
I know some of you speed freaks would have done this in 40 minutes but it took me a couple of days.


New board.jpg
 
Looking Good there!! Have you ever considering installing Slotted Panel Trunking to inside of the DB instead of cable ties around the cabling?? I always do this and think it looks neat, and a lot easier if need to trace cables out at a later date.
Not a critisism just some of my knowledge and learnings from over time.
Regards Darren
 
Rough and missing terminal numbers, just rough copies before a proper computer drawing neat and standardised. Pretty basic circuit as you can see but I thought I'd share

This is just a control panel for a Plasma Nitrider. The complicated side of this machine is all in an Electronic Circuit (which I have the drawings for if anyone is interested) it's packed full of inverters and rectifiers. The more complicated stuff comes with the Arc Detection parameters. My company had a Romanian Physicist custom make it for us, he apparently works on the LHC now lol.

IMG_1924.jpg

Just a quick update, getting there, just doing bits and bobs when I can. Not as pretty as I'd like lol but getting rushed to do things, have to show progress while dealing with other breakdowns and what not. Also I duno what's happening with my photos lol
 

Attachments

  • IMG_1924.jpg
    198.9 KB · Views: 396
Last edited by a moderator:

Reply to **Show Us Your Installs!!!** in the Australia area at ElectriciansForums.net

Similar Threads

Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
491
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I'm unsure if I should be an electrician or maybe another trade is better. I have basically completed my first year of a foundation in...
Replies
9
Views
762
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top