Discuss Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Presume you mean Zs? so as per post#2 what is the Ze?Ze of 2.42.
Connections look all clean and tight with origin reading 0.16Sounds a bit high a reading to be due to just the cable resistance? What is Ze at the supply origin? Perhaps poor or corroded connections of the armour?
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great
Thank you DefyGPresume you mean Zs? so as per post#2 what is the Ze?
yesIs this the same 100M cable as the one in the link in post #4?
Reply to Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net