So should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?

I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
 
Didn't you get an IR reading of 0.7M between two of the conductors?
I did. Have since gone back withnewly calibrated tester and done a new clean test. Its quite concerning that the reading is so different. The 63a mcb at origin has tripped out several times but not recently.
 
So should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?

I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
cable in ground approx 25 years
 
Do some continuity tests to establish where continuity is amiss.
R1+R2, R1+Rn, R2+Rn.
 
Last edited:
Ze o
Connections look all clean and tight with origin reading 0.16
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great


You don't appear to be clear with the problems here.

You talk about insulation resistance of 2.36 to 4.27 - is this Mohm?

This is irrelevant to the Zs

You don't appear to know the differences between insulation resistance, Ze and Zs.

If you do have Ze of 0.16 ohm at the feed end of the cable and ~2.5 ohm at the load end, there is absolutely something wrong with the cable or terminations.

I would expect a r1 + r2 of 0.5 ohms or thereabouts.

You need to find this fault, not cover it up by adding rods or anything else.

You need to measure the r1 + r2, the r1 + rn etc. This will show if you have a cable fault. And will identify which conductor is the problem, if they all read 0.5 ohms (less for r1 + rn) then the fault is between the cable feed end and the header. - most likely a bad connection in the earth path.
 

Reply to Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top