Didn't you get an IR reading of 0.7M between two of the conductors?
Discuss Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
measuredSo Ze is 0.16 and Zs is 2.42. Is this measured or calculated by continuity.
I did. Have since gone back withnewly calibrated tester and done a new clean test. Its quite concerning that the reading is so different. The 63a mcb at origin has tripped out several times but not recently.Didn't you get an IR reading of 0.7M between two of the conductors?
cable in ground approx 25 yearsSo should be looking at a Zs reading of 0.16+0.49 = 0.65? (when energised, but presumably this is an old unused cable) so sticking with expected R1+R2 for now should be 0.49ohms?
I could understand high L-E and N-E measurement if corroded swa at gland or similar but that shouldn't affect L-N measurement which should be about 0.23ohms! unless something amiss with cable?
What IR readings are you getting now?Its quite concerning that the reading is so different.
Connections look all clean and tight with origin reading 0.16
Ins res L-E 3.37, N-E 4.27
and N-L 2.36 so not great
The Zs for the socket circuit is not relevant your problem is the submain.Thank you DefyG
Ze at origin 0.16, zs at annex csu 2.42, total zs on socket circuit 2.67
Ins res L-E 3.37, N-E 4.27What IR readings are you getting now?