EICR Code for no main earth
M
mamba
Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
If you mean the Main Earth Conductor? I found one missing on a Periodic once at a Pharmacy in Bradford, so I just fitted one and moved on. I was on wages at the time! :-)
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
It is not an immediate Danger, it would take a second fault (L to E) to become so, hence a C2 potentially dangerous, Niccy don't write the rules they just like to think they do.
i'd agree with a C2 as it would require a fault ( live part to exposed part ) to present a danger.
It all depends on the circumstances No main earth not a good one most situations it would be a C2 i have come across a similar situation where there was an induced voltage of 85 volts in that scenario i would give it a C1
Yep ditto the above. Quite often find induced voltages of that size.. Nowhere to go without the main bond..!
Another way of looking at it...is that it is a very high impedance voltage source.
So the reading depends on the input impedance of the test voltmeter.
Also, why it it doesn't present a shock hazard.
C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
mamba,
Eddiesparks,
