What does it say in the Best Practice Guide No 4 about plastic CU's?
Are we not working to BS7671?
I can't find anywhere in BS7671 that states we should refer to Best Practice Guides.
As stated above, there are thousands of plastic CU's. To code them for just being plastic is wrong IMO.
If you are going to code plastic CU's then you have to code surface mounted cables that don't have adequate support against a fire.

Which I would do.
 
All you are saying with a C3 is that a significant improvement to safety can be acheived by in this case making the surrounds or consumer unit fireproof. Personally I feel if it is under a stairs an important escape route could be compromised if a fire started under it. I don't know about you but I would not be happy with that potential risk in my home especially with kids about, being serious for a moment!

Whilst the inclusion of metal boards has reduced fire risk (for whatever the actual reason plastics suddenly became a risk)

The number of incidents of molten dist boards (when installed correctly) must be minuscule,the potential risk would reflect that
Life is full of risk,its good to reduce that risk but lets not go over the top:eek:
If the board is installed correctly and/or correctly inspected, the risk is likely to be as low as its ever going to be compared to a new one even if it were made from asbestos :rolleyes:
 
My view on this as you are giving someone a professional opinion on their installation as of the date of inspection. I would therefore give a C3 whatever the location. A metal consumer unit would now be fitted if this was a new build property and therefore an improvement could be made/recommended. Should there be a fire within the CU/house at a later date and it was not contained and caused damage or serious injury or death the owner/householder/insurer/courts could state that you did not draw to their attention that this was an area where improvement could have been made to their installation. Cables in escape routes are not normally visible so would surely be a lim. An old boss of mine always used to say to me, when you make a decision you should firstly consider what it would read like on the front page of the Sun or when reported in the local news when it all goes horribly wrong!
 
One of the problems I have with this Consumer Unit issue, is that it is not the Wiring Regulations that should have changed, but the BS EN standards that relate to Consumer Units.
Of course, what has happened, is that both have changed.
 
Wish there was so much open discussion and debate on whether me ball joint on me van was a pass or a fail, on its mot last time out.

If none of you can agree on this one point, how do you agree on the rest of the book?

Incidentally, once you've obtained an EICR course or training, at what point can you start giving your competent judgmental opinions; straight away, few months experience or when you're old & crusty like Westwood, no offence Westy. :)
 
Wish there was so much open discussion and debate on whether me ball

Do not want to discuss your balls..

If none of you can agree on this one point, how do you agree on the rest of the book

My post is my personal opinion. I do not do EICR's so it doesn't affect anyone really. Just shocked to think that anyone would even consider giving a CU a C2 just because it's plastic.
 
Do not want to discuss your balls..



My post is my personal opinion. I do not do EICR's so it doesn't affect anyone really. Just shocked to think that anyone would even consider giving a CU a C2 just because it's plastic.
Bang on, Spoon
 
Life is full of risk,its good to reduce that risk but lets not go over the top
It is hardly "going over the top" bringing to the attention of a home owner a potential risk it is more by way of advice it is not as if it is a judgement from the Lord high executioner it is simply sage advice. The fact the risk as perceived by you @Des 56 is miniscule does not detract from the fact that certain professional bodies have deemed it a risk who are in a better position to assess that risk certainly more so than mere personal opinion and subjective conjecture. I see no reason to fly in the face of that and refuse to acknowledge and inform others who can then make their own decision as to how to handle it.
 
so, a plastic CU that's properlyinstalled gets a C£ code. Customer then decides to have it replaced with a metal CU.This is done by a wet-behind-the -ears Electrical Trainee, with loose terminations, ropey cable dressing, and an indecipherable EIC. and you call that an improvement???
 
It is hardly "going over the top" bringing to the attention of a home owner a potential risk it is more by way of advice it is not as if it is a judgement from the Lord high executioner it is simply sage advice. The fact the risk as perceived by you @Des 56 is miniscule does not detract from the fact that certain professional bodies have deemed it a risk who are in a better position to assess that risk certainly more so than mere personal opinion and subjective conjecture. I see no reason to fly in the face of that and refuse to acknowledge and inform others who can then make their own decision as to how to handle it.
Have you been at the Dictionary again this morning Tel, all these big words and precise statements?
 
so, a plastic CU that's properly installed gets a C3 code. Customer then decides to have it replaced with a metal CU.This is done by a wet-behind-the -ears Electrical Trainee, with loose terminations, ropey cable dressing, and an indecipherable EIC. and you call that an improvement???

You forgot.... Then come January all the circuits going into the CU get a C3 for not having any AFDD's
 
This is done by a wet-behind-the -ears Electrical Trainee, with loose terminations, ropey cable dressing, and an indecipherable EIC. and you call that an improvement???
Installations by incompetent persons is a different matter to coding a plastic CU. I usually advise customers to fireproof the stairs themselves rather than change the CU. I often see understairs packed to the gunnels with property. And the wooden understairs is exposed looking like it would go up like a tinder box. Remember that a C3 is not compulsory it is advisory, surely there is no harm in advising where there is a risk?
 
My post is my personal opinion. I do not do EICR's so it doesn't affect anyone really. Just shocked to think that anyone would even consider giving a CU a C2 just because it's plastic.

But, present company accepted, that's just the point. For someone who does EICR's, it should not be opinionated.

A plastic CU, in a domestic property, under the stairs should either be a C2 or a C3, or whatever stupid code, or not at all. It quite a specific set of circumstances, and doesn't vary from one property to another. Seems that various property owners, across the country would get different assessments for the exact same scenario.

I don't do EICR's either, kinda glad I don't.
 
You forgot.... Then come January all the circuits going into the CU get a C3 for not having any AFDD's
I would doubt that. I believe they are only coming in as advisory in January. Not got my blue book yet though so correct me if wrong.

Just to ease your mind, the BPG only recommends a C3 for combustible boards situated in sole escape routes, and a no code if not. I personally think that is quite sensible guidance.
 

Reply to EICR - PLASTIC CONSUMER UNIT CODE C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Had a quick look this morning as it’s local. It’s a full rcbo starbreaker installed in the kitchen pantry but unfortunately it’s plastic...
Replies
10
Views
2K
i notice you mention "fire rated" instead of "metallic" Are we talking about a metal consumer unit? I know its presumed... but just checking
Replies
4
Views
622
I agree, it's not an immediate danger so can't be a C2. Bad design though, so improvement recommended.
Replies
4
Views
3K
I’d be more concerned about those blanking clips on the main CU.
Replies
24
Views
3K
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks