Hi mate,
I will likely be be shot at for this post, but here goes,
In this situation, where you are constrained as you are,
I would, feed your 16mm armoured with a 32mA MCB, your lighting circuit distribution cable in 2.5mm, and maybe split that into two 10M runs, the two cables can be 'junctioned' at the 6A MCB/RCBO, ie. terminated at the shed DB, and then stick your socket circuits (length ?) on either a 2.5mm ring, or 4mm radial fed from a 16A MCB/RCBO, or even two seperate 4mm radials, again both runs can be terminated at the MCB, this would give you the discrimination required, ie. if the sockets tripped, you would still have lighting.
Provided your disconnection times and Zs is within bounds this would then be the safest option.
If the VD is a little on the High side for the lights calculated, you could apply diversity, and maybe reduce the calculated maximum current demand, bearing in mind you will not be using either the full 6A for the lights, and you may not be using the full 32A for the sub-main either, these protective devices are providing the required protection for the cables to the circuits, and the RCD protecting the sockets, the CCC is not in doubt here either, this installation will be the best you can achieve in the circumstances.
I know in an ideal world all of this would be calculated before you started, but in reality we often have to do what is expedient, the main thing is,
is it safe ?
If the answer to the above question is yes, then you are good to go IMO, so what if the VD maybe is a little high on the lights
if the the circuits were used to the full capacity, this is ultimately a design decision, and at the very worst you
may have exceeded the VD on the lighting circuit by a small amount, but to me this is the least onerous rule you could possibly break here, then there is rule 525.4 which will give you a little leeway.
At the end of the day apply some common sense.
Not much sleep lol one other thing that come to mind is 3% of supply voltage 242v= 7.2v ?
sorry mate, all calcs at 230V
What Iam getting at here is, don't try and 'fudge' your calcs, only you know the design requirements, and how the installation is to be used.
Make your design decisions based on the available info., and run with that, what you cannot do, is to get someone else to say this is okay, neither me nor anyone else can tell you to break a rule, you need to justify the design decisions you take.