Yes, last sentence of 542.2.6 -Other metallic water supply pipework shall not be used as an earth electrode unless precautions are taken against its removal and it has been considered for such a use.
Thank you for that,nice.
Non-statutory, yes but you can be prosecuted by refering to them hence the reason we have to be updated on them whenever there is a change.
You can argue as much as you want and dismiss advice here.
The op who posted wanted guidance and if he is going to sit his AM2 and does that he is going to fail.
The issue of you not having the guidance note is your problem ,you can choose to refer to as many books and notes as you wish.
The...
Section 54
It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.
He should tell us what the rating for the protective devices are.
Just mentioning 30mm RCDs is not enough
What are the type of circuits these fridges are on?