2.5mm | Page 5

2.5mm

  1. G

    multi strand 2.5mm T&E - is it OK to use?

    Hi, I've been working in a relatively new house (approx 5 years old) and the kitchen ring is wired with 2.5mm, twin and earth in which both the line and protective conductors are multistranded. Is this OK to use? I've never come across it on 2.5mm cable and they have nuisance tripping on this...
  2. B

    2.5mm bonding

    Carrying out a PIR on a large retail outlet I checked the bonding to the pipes under the sink in the kitchen area which were cross bonded with 2.5mm. What is the minimum size the cross bonding should be? The main earth to the board is 100mm!!!
  3. S

    2.5mm and 4mm in same ring - acceptable?

    As per the title. And if so, what would you put on the schedule of test results? (One end of the ring is 2.5mm and the other 4mm - so it is obvious at the CCU). I am assuming it is 4mm. It is old colours (black and red) and the conductors are stranded so I'm thinking it's not 2.5mm. The...
  4. G

    2.5mm radial

    I have a basement that has 2 rooms. 1 has power and the other has not. I installed a 2.5mm ring in the room with no power, comprising of 8 double sockets. When I went to add these to the ring in the other room I discovered that there is no ring, it is actually a 4mm radial circuit on a 30 amp...
  5. D

    2.5mm used for lighting circuit.....

    Hello chaps Did a visual safety check at a house today. All seems ok, except for the lighting circuit. Who ever installed/re-wired the system has used 2.5mm cable.....to me it seems a bit overkill, but could this be used to try and cover an issue that its previously had. Is this ok? Not...
  6. C

    32A mcb on a 2.5mm cable

    Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do...
  7. R

    9.5kw shower, 2.5mm cable.....

    got a call earlier this week from someone asking me to look at there shower as they had had an electric shock from it. intially advised them to switch of at pull switch, (not able to do so in fuse box as it was ild wylex 4 way and not marked up, customer unsure how to pull fuses etc)...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top