32a

  1. B

    Design 32a 4mm radial

    Good morning I wonder if I could have some confirmation in regards to a radial circuit. I have been showing apprentices different methods if wiring ring and radial circuits. I wish to continue this next week. I can not see any regulation not permitting the drawing enclosed, I would just like...
  2. T

    32A Timer for Hot tub

    Hi, I'm trying to find a timer control, or smart switch for a 32A circuit. It is for a hot tub which is expensive to run. I want the hot tub to only heat during the cheap electricity hours overnight. There are loads of 13A timers on the market, but the only 32A ones I can find are ones that...
  3. HappyHippyDad

    32A or 40A circuit breaker?

    A really simple question. I'm sat here with my coffee and getting confused by it! 7.4kW EVCP. Would I fit a 32A or 40A RCBO? Not concerned with anything else, as it's all sorted, but the fact that the 7.4kW equates to 32.17A has thrown me. I was just going to use a 32A RCBO, but really I should...
  4. S

    4mm2 for 32A

    Hi, I have an incoming 32A single phase supply to a 16A equipment. To protect the equipment I installed a 16A MCB in between. My question is for the cable from 32A MCB to 16A MCB, can I use 2+e x 2.5mm2 cable? I know for 32A we are supposed to use 4mm2 cable, but the electrical shops nearby...
  5. I

    32a mcb on a 2.5m radial

    Is the above OK, its feeding a fused spur downstream with a combi boiler attached to the spur. Cheers
  6. Mark42

    32A single phase output from 3 x 16A three phase supply. Is there a way?

    I have a workshop in a remote location which I rent out. The incoming supply is 3 x 16A three phase on 180m of 16mm SWA. An upcoming customer has a machine which needs a 32A single phase supply. (Actual load about 25A.) The energy is there, but it's split across the three phases. Is there some...
  7. K

    Can ring circuit be bigger than 32A with bigger cable size??

    Hi everyone my questions is regarding a ring circuit wired in 2.5mm standard twin n earth with 32A MCB however my question is hypothetical if there are 2 laundry and 2 lets say tumblers so load is not suitable for the circuit and you want to upgrade but there is no space in consumer unit to...
  8. S

    2.5mm2 cable with 32A isolator

    Hi guys, I am going to install a device, it is running microwave magnetron up to 2kW, with power supply of 230V/Single phase/ 50Hz. According to manufacturer's instruction, it supposed to be connected to a 16A MCB/isolator for protection. The problem now is that the location only has a 32A...
  9. C

    Lighting circuit supplied from a 32A ring main socket.

    Hi guys, I am adding a lighting circuit to a Ring main 32 A. Can I just use a 6A MCB type B in a box on DIN rail to supply my lighting. I am using 1.5mm cable after the 6 A MCB. Thanks for your advice!
  10. G

    2 x 32a supplies into my fusebox on boat.

    I'm a novice but willing to learn. Go easy on me! re above. I have upper and lower rooms. Should I run two socket circuits or one? Total double sockets I have is 20. Boat is 15m long, 4m wide.
  11. J

    16A off 32A ring

    How do you guys get over taking an appliance which is 16A off a 32A ring? thx
  12. D

    32A to 2x 16A

    I am currently looking at installing some equipment in a small IT comms room and am looking for some advice on the current setup and how to proceed, I am not an electrician myself. 1: Currently there is a 32A supply being fed directly into PDU with 13A sockets, same as the the link below, my...
  13. S

    UK 32a supply for a hot tub of a PME supply.

    Hi there, I have been asked to install a 32a supply for a hot tub for a client. I haven’t installed a supply for a hot tub before and having done a bit of research I am getting mixed answers about doing this on a PME system. I have a DB under the stairs with plenty of spare ways so I would be...
  14. J

    4mm radial from 2.5mm ring on 32A?

    Go easy I’m new to this but.. I’ve just come across a 4mm radial (garage) being fed from downstairs 32A MCB ring. Trying to locate the connection but question is does this comply with BS7671? I can’t tell if it’s on a 13A FS or not at the moment.
  15. J

    PAT testing 32A cable

    We have some 32A extension leads that range from 5m to 20m, I'm struggling to find what the acceptable values are for the resistence test. The PAT tester has a built in calculator, but that only goes up to 4mm cable, this is using 6mm. Where can I find the information I need to get the pass...
  16. L

    Where to install 32a socket

    I need to install a 32a single phase socket next to a water outlet. I am thinking of putting it roughly 2 foot above and a foot to the left of the outlet. I haven’t got access to my regs to can’t check if this is enough distance? Any help appreciated. Lewis
  17. J

    230/240vac 10.5a rated heat plate into Single Ph 32a commando socket

    Hi all, ist post: I have a portable appliance which is a temperature controlled heat plate, the input requirements are single phase 230/240vac 10.5a, the unit is designed and built in the US and is factory adapted for the UK market. The supplied flex that comes with the unit is 3.3 mm sq 3 core...
  18. X

    Using an old 32A shower circuit for new sockets.

    Nearly fifteen years ago I moved a bathroom in our house, and repurposed the 32A electrical shower circuit to power a pair of double sockets - which then had multiway adaptors powering all my office hardware (i.e. low overall power). Not exactly complex or risky at the time, and the MCB has...
  19. haptism

    Gland for MK 32A commando plug

    Anyone know what gland for is needed a MK 32A commando socket to hold a flex ??? Its got a thread for a gland (see pics) I expect its a stuffing gland if using flex but its an odd size. Its for a commercial single phase oven 16Kw
  20. W

    Grid switches on 32A ring

    I've been trying to work out whether grid switches (ie. a 20A switch) are acceptable on a normal 32A ring. I've read many threads online. Very few people seem sure whether it's acceptable but many sparks seem to do it in kitchens etc. The argument seems to be that the switch is rated at 20A but...