  1. M

    re routing armourd cable from 32a hot tub

    Hi have a TT CU in property with RCDs, Earth strap appears fine and solid. A 25meter cable has been run from RCD as a single 32 amp cct to a hot tub that is no longer present.. I want to reroute the cable to a garage for lights and sockets. The main question is do I need to use another RCD...
  2. Z

    Question regarding signing off 32a ring circuit with broken CPC ring continuity

    I installed a kitchen ring recently. Went back to test after the builders had finished and found that the CPC is broken somewhere inaccessible, everything else tests normal. I’ve got continuity on live conductors, and even with the broken CPC, each socket is connected to the CPC and tests with...
  3. P

    Single phase appliance from a 32a 5 pin trailing socket

    Hi all What are the thoughts on fitting a male 5 pin plug to a single phase appliance then connecting it to a 5 pin three phase socket. Obviously only using one phase. Rough but as a temporary measure is it against the regulations? Found these distribution boxes which appear to do similar...
  4. gazdkw82

    Ax disconnection times 32A+

    I don't know why I've not noticed before but the disconnection time for final circuits greater than 32A is 5 secs on a TN earthing arrangement. Does that mean a shower has a disconnection time of 5 secs? Although this circuit would also fall under protection of an RCD?? Also, cooker circuits...
  5. B

    6mm 32A radial to supply 2 3.65kw 16a ovens

    Hi, Doing wiring for a kitchen co. Done plenty of these recently, but we've been doing all wiring from scratch and have just run 16a radials direct from board. In this instance it's a ballache to run back to board, and I've got a perfectly decent 6mm cable from board to oven location. I'm...
  6. M

    32A MCB feeding 1.5mm & 2.5mm T&E cables via 30A terminal block

    Quickie - Would you say this is ok? 32A MCB feeding 6mm T&E which is then connected to a 2.5mm T&E & 1.5mm T&E cable via a 30A terminal block in plastic terminal block housing buried in stud wall. The 2.5mm feeds a 3kW immersion heater with 13A SFU at the heater end. The 1.5mm feeds gas boiler...
  7. Cornish1984

    Five core 32A 400v sea cable calculation help

  8. F

    32A commando socket without isolator

    Any issues with installing one of these without an isolator? The D.B is about 3 meters away and the commando socket will be mounted under a kitchen worktop for a coffee machine and there isn't enough room for an isolator.
  9. M

    How to thoroughly test a new 2P+E 32A socket

    We are currently having a new office fitted out. It will include a 2P+E 32A socket (Gewiss Interlock Socket 32A 230V 2P+E - https://www.eleconline.co.uk/zdriverel/form/catsel/INDUSTRIAL-PLUG/SKTS/product/M1643) for our UPS. I want to run my own tests in advance of moving in, to be completely...
  10. S

    Mobile equipment not exceeding a rating of 32a for use outdoors.

    Could someone please give me examples of what this would cover. I'm assuming it's irrelevant to portable equipment like a lawn mower on a domestic installation and more to do with industrial. Thanks in advance.
  11. J

    Fitting a hob and oven on the same 32a....

    Hi guys, So i've ditched my 20 year old tricity bendix cooker. Bought a new hob and a single oven and am currently in the process of getting them fitted. I currently have a dedicated cooker circuit, 32a and 6mm. Switch above the worktop and 2 outlets running off it, a hard wired one and a plug...
  12. kingeri

    2.5mm on 32A MCB

    Just wondering what folks would do if you came across this on your travels. 4mm radial sockets circuit, on 32A MCB. Two branches from the CU, one supplying 6 double sockets, wired entirely in 4mm, so fine. The other branch consists of a 1m run of 4mm to a double socket, then around 5m in 2.5mm...
  13. J

    Replacing single 13a plug in oven with 16a fixed wire on 32a dedicated circuit

    Hi all, Thank you in advance for your help. This is my current setup: 32a MCB to 45a CCU with 6mm^2 wiring (no additional socket at CCU) 6mm^2 wiring to two separate sockets behind kitchen units (one for gas hob ignition one for 13a plug in oven, nothing else on circuit) My new oven is 3640W...
  14. kingeri

    4mm 32a Radial In Trunking

    Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to...
  15. D

    Feeding new 2 way board from 32a MCB

    Hi all, OK, so was sent to a job today for upgrading a kitchen. The existing mains was an older MEM board which the newer Eaton RCBO's wont fit. The only circuits being amended are the kitchen ring main (32 amp) and the lighting circuit (5 amp). The customer would not have been keen on...
  16. C

    Cable To Use For A 32A Commando socket!

    So I have some servers in my shed and I simply can't run all these servers of a single 13A socket so I need to change my power solution here's a design I mocked up, I'm just wondering what cable to use from the consumer unit to the commando plug in the shed, The MCB is 32AMP so I'm just curious...
  17. C

    Ka Rating of 32A BS88 gG AT 400V/ 230V AC???

    Hi, I am trying to determine the Ka rating of the above fuse. For 400V I believe it is 80 Ka but have found that it is 40 Ka for 250V DC. Can anyone tell me what it is for 230V AC or where I can find the answer? I have already looked on the web and in the latest OSG but maybe not in the right...
  18. T

    maximum devices for 32A ring

    Hi all We are setting up a IT training company and we are trying to work out how many devices he can have in training room. There are 5 double sockets in the room, and they all go back to a 32A fuse. We want to have the following in the room, will this be ok with the fuses/amps etc. 45W...
  19. S

    Max Zs on rcbo type c 32a 1667 or 0.54??

    Has anyone any views on max Zs for say a type c 32a rcbo at 80% is 0.54 and 100% 0.68. I am currently testing a collage and all ring circuits are type c and I am exceeding 0.54 and 0.68 this is a TNCS system so to my knowledge table 41.5 in regs which tells us 1667 for 32a rcbo for TT systems...
  20. J

    Why is a cooker circuit generally 6mm and 32a

    As above why is this as I have had a thought and a 20a 2.5 mm cable would be sufficient? Even in my new built it has an oven and hob both 32a radials for each on 6mm cable? Each with a 13a plug on the appliance as diversity shows around 10a max. so even with an upgraded appliance I don't see...