32a

  1. yellowvanman

    6mm T&E on a 32A Cooker circuit

    Struck me recently as to why we use 6mm T&E for a 32A cooker circuit, when generally 4mm (clipped direct) would be sufficient. Is this a historical thing with BS3036 fuses?
  2. J

    32A external socets and rcd protection

    Hi can somebody give me some help with this one, a yard for porta cabin storage and external 32A sockets fixed around the perimeter although the sockets are rated at 32A they have 16A mcb's fitted in the enclosure. leads are then run out to test the cabins and do maintenance,although the cabins...
  3. J

    kitchen 32a rfc or 2x a3 radial

    Just thinking about a kitchen circuit, How close would i be pushing a 32a rfc with washing machine, dishwasher, and two double sockets (likely to use kettle and toaster at the same time ) would 2x A3 circuits be more sensible?
  4. richy3333

    Lights spurred off a FRC and protected by a 32A MCB

    Working on an installation today. Noticed a circuit which is not connected to my work (different circuit). 1.5mm T&E (Ref method A) for upstairs lights fed off (I presume a hidden JB as nothing is visible) a FRC and protected by a 32A MCB. It's not been fused down, at least no FCU visible. No...
  5. R

    32A mcb changed to 40A mcb what certs?

    Hi I was wondering what certificate is required for changing just one 32A mcb to 40A mcb. It for 8.5 kw shower replacement, 15 meter of wiring is existing 10mm2 clipped to wall and there is a 45A shower isolator in meter cupboard.
  6. spud1

    No RCD protection for socket outlets rated 32A or greater

    Hi Guys, Can somebody shed any light on why socket outlets rated at 32Amps or greater do not require RCD protection under BS7671? Presumably theres some maths behind it? And presumably the only exception is in a TT earthing System? Cheers chaps
  7. N

    32A ring circuits wired in 1.5mm firetuf

    I've been asked to inspect a shop and have found 4x 32 amp ring final circuits supplying socket outlets, all wired in firetuf 1.5mm twin and earth. Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers.. My concern is does this comply with 421.1.103...
  8. G

    32A mcb supplying 32A 30ma rcd unit next to db

    Hi as title says my engineer wants me to fit the above to protect ring circuits supplied from a crabtree c50 board, wants me to supply a rcd unit from a 32A mcb with 4mm singles and then supply the ring from the 32A 30ma rcd, I think the reason for doing this is either you cant get crabtree c50...
  9. Traineenoob

    Spur on 32a BSEN 61009

    Hi Can i spur from a 32A ring final at the mcb with 2.5mm t&e? Is this within the regs? I think it is but just want clarification pg 159 osg says you can connect at the distribution board. Thanks
  10. W

    TT Max ZS loop reading for circuits over 32A

    HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A Anyone enlighten me, i need it for a 50A and 40A circuit?? thanks
  11. B

    32A mcb 36A load

    Hi all on a periodic how many of you would code 4 a shower drawing 36A protected by a 32Amcb just dont want to be to picky but i feel it should be noted to cover my back
  12. S

    Lighting Circuit On 32a Mcb - Help Required Please

    Hi everyone, Can someone please help me. A local house wanted some emergency lighting putting in so when i went and had a look at the consumer unit it had the upstairs lighting circuit on a 6A mcb and the downstairs on a 32A mcb. The CU has NICIEC stickers all over it. Am i missing something...
  13. S

    2 Radials into a 32A B type breaker and other wonders !!!

    Hi all, Hope you guys are all enjoying the nice weather and not working inside some dark small cupboard like I was today !!!! Anyway, here is the scenario. Neighbour comes over this morning and says her fuse for downstairs has tripped and cannot be re-set. I go and take a quick look and test and...
  14. R

    32a busbar feeding floorboxes

    Should the busbar be fed via an rcbo or not
  15. S

    Fitting 240V 32A commando

    Hi we have a welder which can pull upto 32A according to the spec. It says I(max) 32A. The circuit to the garage has a 16A MCB at the consumer unit. It's only powering two double sockets however am going to add a commando. So I wondering if 32A MCB would sufficient or would it have to be bigger...
  16. R

    32a 3 phase extension lead.

    My dad wants me to make him an extension lead. Currently a 32A 3 phases soscket on a genrator. He has severral different loads ( all motors) but there total loads are about 20A Use some braided SY cable. 4mm 4core or 5 core? I guess its better to have a seprate earth core so 5 core.I need...
  17. J

    RCBO 32A problem testing

    hi guys i am working from consumer unit with swa 2.5 just but a double socket in. but when i am ZS testing the max is coming back at 15.33 - 15.36 checked all wiring and all corrects rcbo not faulty any ideas.
  18. M

    Size of Flex for 32A CEE / Comando Plug to 2 x 16A CEE / Comando Trailing Sockets

    Hi Guys, Firslty i'm new to the forums so hello and hope you're all doing well. A quick question on the size of the HO7 flex I need to use for a splitter that will have a 32A Comando Plug on one end and two 16A Sockets on the other. Would I be right in saying that each split will need 2.5mm...
  19. C

    Contactor ok for 2 x 32A rings?

    I've never designed or installed using contactors before but a client has just asked if they can have a keyswitch to knock off 2 ring circuits in an office at the end of the working day. There is currently a small 5 way board with 3 spare ways and 2x 32A RCBOs for the 2 ring circuits. My...
  20. C

    32A mcb on a 2.5mm cable

    Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do...