Struck me recently as to why we use 6mm T&E for a 32A cooker circuit, when generally 4mm (clipped direct) would be sufficient. Is this a historical thing with BS3036 fuses?
Hi can somebody give me some help with this one, a yard for porta cabin storage and external 32A sockets fixed around the perimeter although the sockets are rated at 32A they have 16A mcb's fitted in the enclosure. leads are then run out to test the cabins and do maintenance,although the cabins...
Just thinking about a kitchen circuit, How close would i be pushing a 32a rfc with washing machine, dishwasher, and two double sockets (likely to use kettle and toaster at the same time ) would 2x A3 circuits be more sensible?
Working on an installation today. Noticed a circuit which is not connected to my work (different circuit). 1.5mm T&E (Ref method A) for upstairs lights fed off (I presume a hidden JB as nothing is visible) a FRC and protected by a 32A MCB. It's not been fused down, at least no FCU visible. No...
Hi I was wondering what certificate is required for changing just one 32A mcb to 40A mcb. It for 8.5 kw shower replacement, 15 meter of wiring is existing 10mm2 clipped to wall and there is a 45A shower isolator in meter cupboard.
Hi Guys,
Can somebody shed any light on why socket outlets rated at 32Amps or greater do not require RCD protection under BS7671?
Presumably theres some maths behind it?
And presumably the only exception is in a TT earthing System?
Cheers chaps
I've been asked to inspect a shop and have found 4x 32 amp ring final circuits supplying socket outlets, all wired in firetuf 1.5mm twin and earth.
Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers..
My concern is does this comply with 421.1.103...
Natt
Thread
32a
alarm
cable
capacity
circuit
circuits
consumer
current
electricians' talk
fire
ring
wired
Hi as title says my engineer wants me to fit the above to protect ring circuits supplied from a crabtree c50 board, wants me to supply a rcd unit from a 32A mcb with 4mm singles and then supply the ring from the 32A 30ma rcd,
I think the reason for doing this is either you cant get crabtree c50...
Guest112
Thread
30ma
32a
aus
circuit
crabtree
current
electricians' talk
mcb
rcd
supplying
unit
Hi
Can i spur from a 32A ring final at the mcb with 2.5mm t&e? Is this within the regs? I think it is but just want clarification pg 159 osg says you can connect at the distribution board.
Thanks
HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A
Anyone enlighten me, i need it for a 50A and 40A circuit??
thanks
Welchyboy
Thread
32a
circuit
circuits
disconnection
electricians' talk
loop
max
reading
Hi all
on a periodic how many of you would code 4 a shower drawing 36A protected by a 32Amcb
just dont want to be to picky but i feel it should be noted to cover my back
Hi everyone,
Can someone please help me. A local house wanted some emergency lighting putting in so when i went and had a look at the consumer unit it had the upstairs lighting circuit on a 6A mcb and the downstairs on a 32A mcb. The CU has NICIEC stickers all over it.
Am i missing something...
sparky1966
Thread
32a
circuit
circuits
electricians' talk
help
lighting
lighting circuit
mcb
other
please
required
Hi all,
Hope you guys are all enjoying the nice weather and not working inside some dark small cupboard like I was today !!!!
Anyway, here is the scenario. Neighbour comes over this morning and says her fuse for downstairs has tripped and cannot be re-set.
I go and take a quick look and test and...
Sav
Thread
32a
aus
breaker
conservatory
electricians' talk
explain
kitchen
other
radials
sockets
type
Hi we have a welder which can pull upto 32A according to the spec. It says I(max) 32A.
The circuit to the garage has a 16A MCB at the consumer unit. It's only powering two double sockets however am going to add a commando. So I wondering if 32A MCB would sufficient or would it have to be bigger...
My dad wants me to make him an extension lead. Currently a 32A 3 phases soscket on a genrator. He has severral different loads ( all motors) but there total loads are about 20A
Use some braided SY cable. 4mm 4core or 5 core? I guess its better to have a seprate earth core so 5 core.I need...
Robo
Thread
3 phase
32a
aus
electricians' talk
extension
extension lead
lead
leads
loads
phase
sockets
hi guys i am working from consumer unit with swa 2.5 just but a double socket in. but when i am ZS testing the max is coming back at 15.33 - 15.36 checked all wiring and all corrects rcbo not faulty any ideas.
Hi Guys,
Firslty i'm new to the forums so hello and hope you're all doing well.
A quick question on the size of the HO7 flex I need to use for a splitter that will have a 32A Comando Plug on one end and two 16A Sockets on the other.
Would I be right in saying that each split will need 2.5mm...
I've never designed or installed using contactors before but a client has just asked if they can have a keyswitch to knock off 2 ring circuits in an office at the end of the working day. There is currently a small 5 way board with 3 spare ways and 2x 32A RCBOs for the 2 ring circuits.
My...
Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do...