Hi
Can i spur from a 32A ring final at the mcb with 2.5mm t&e? Is this within the regs? I think it is but just want clarification pg 159 osg says you can connect at the distribution board.
Thanks
HI all anyone know the above, i put 1667 ohms in the box normally for all TT circuits but noticed the other day it is only for circuits upto 32A
Anyone enlighten me, i need it for a 50A and 40A circuit??
thanks
Welchyboy
Thread
32a
circuit
circuits
disconnection
loop
max
reading
Hi all
on a periodic how many of you would code 4 a shower drawing 36A protected by a 32Amcb
just dont want to be to picky but i feel it should be noted to cover my back
Hi everyone,
Can someone please help me. A local house wanted some emergency lighting putting in so when i went and had a look at the consumer unit it had the upstairs lighting circuit on a 6A mcb and the downstairs on a 32A mcb. The CU has NICIEC stickers all over it.
Am i missing something...
sparky1966
Thread
32a
circuit
circuits
help
lighting
lighting circuit
mcb
other
please
required
Hi all,
Hope you guys are all enjoying the nice weather and not working inside some dark small cupboard like I was today !!!!
Anyway, here is the scenario. Neighbour comes over this morning and says her fuse for downstairs has tripped and cannot be re-set.
I go and take a quick look and test and...
Sav
Thread
32a
aus
breaker
conservatory
explain
kitchen
other
radials
sockets
type
Hi we have a welder which can pull upto 32A according to the spec. It says I(max) 32A.
The circuit to the garage has a 16A MCB at the consumer unit. It's only powering two double sockets however am going to add a commando. So I wondering if 32A MCB would sufficient or would it have to be bigger...
My dad wants me to make him an extension lead. Currently a 32A 3 phases soscket on a genrator. He has severral different loads ( all motors) but there total loads are about 20A
Use some braided SY cable. 4mm 4core or 5 core? I guess its better to have a seprate earth core so 5 core.I need...
Robo
Thread
3 phase
32a
aus
extension
extension lead
leads
loads
phase
sockets
hi guys i am working from consumer unit with swa 2.5 just but a double socket in. but when i am ZS testing the max is coming back at 15.33 - 15.36 checked all wiring and all corrects rcbo not faulty any ideas.
Hi Guys,
Firslty i'm new to the forums so hello and hope you're all doing well.
A quick question on the size of the HO7 flex I need to use for a splitter that will have a 32A Comando Plug on one end and two 16A Sockets on the other.
Would I be right in saying that each split will need 2.5mm...
I've never designed or installed using contactors before but a client has just asked if they can have a keyswitch to knock off 2 ring circuits in an office at the end of the working day. There is currently a small 5 way board with 3 spare ways and 2x 32A RCBOs for the 2 ring circuits.
My...
Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do...
I have to use an swa feed from a 32a single phase socket (the ip rated plastic type)
Is there a 32a plug on the market with glanding facility?
The plug will always be in, well almost always. Just unplugged for maintenance perhaps once per year.
I've used the metaflex type with cable clamp...
Can someone confirm longest legth for a ring main using 4mm singles P,N & E that can be run without exceeding max voltage drop or Ze ?
I have a length in mind, but don't wish to appear a ----, so will await some answers and then nod my head in agreement :)
Thanks in advance